Micro-pile skin friction

Micro-pile skin friction

Micro-pile skin friction

(OP)
Hi,

I'm currently doing a design of a steel stepover structure to allow access across a conveyor. The client have requested that they want to use steel stakes/piles to tie the columns directly into a cement stabilised pavement. The standard piles (or stakes rather) are 20mm diameter by 360mm long (embedded depth).

The pile will be taking, as a worst case, 6kN uplift force and approximately 3kN of horizontal force.

I am just wondering if anyone had any ideas of how I could estimate the skin friction between cement stabilised soil and the steel pile. The only information I could find is for piles in excess of 2.5m long.

Any advice would be appreciated.

Regards.

RE: Micro-pile skin friction

That's not a pile, it's a stake...or a toothpick. Why not just use a concrete pad each side?

RE: Micro-pile skin friction

(OP)
As mentioned, the client requested this. I would do a footing or pad if I could. The reason for this tie down system is because the structure will be sitting on an asphalt pavement. They don't want to go digging it up because they'd have to remove sections of the conveyor to do the works and it would become too difficult.

Thank you for your abundance of help though.

Regards,

D. Best.

RE: Micro-pile skin friction

I can see making the stepover in one piece, then pegging it down with something like your tent pegs. How would you get 6kN uplift on something like this?

RE: Micro-pile skin friction

(OP)
From the wind. I may be a tad conservative (probably closer to 4 or 5kN) but when I treat the walkway (3.2m long x 0.75m wide x 2.2m high) as a free standing roof, and using a net porosity factor based on the size of the grating, I calculate a small but not insignificant uplift wind force. I have calculated loads based on AS1170.2 (the Australian wind code).

The load combination I used to calculate the worst scenario reaction forces is 0.9*DL + 1.0 x Wind_hortizontal + 1.0 x Wind_uplift.

Regards,

D. Best

RE: Micro-pile skin friction

Are these to be pounded to depth or bored & then driven?
My inclination is to bore/core to about a meter & then install into grout or epoxy.
Design values will take a bit of conjecture, to define the cement stabilised pavement.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources