Does the NFPA 13 2013 section 11.2.3.2.6 "high temperature sprinklers" apply to Paint/spray booths and/or flammable spray areas? I ask as NFPA 33 / 13 says to use sprinkler temperatures as low as possible BUT a 500ft sq. decrease in calc area sure makes things nice.

RE: Spray booths to Extra Hazard II

I think you can also use 11.2K heads and get the hi temp area reduction.