Calculating crushing imposed by pipe supports
Hi, I have a 600NB Std Wt pipe that is full with water and supported every 5m. My question is whether or not the pipe requires a seat or whether it can just lay flat on a concrete pedestal? Obviously if it is sitting in a rounded pipe seat it would be better due to greater contact support on the pipe, but I am wondering how much better it is, more so out of interest?
If the pipe is lying flat on a plate or concrete pedestal you are basically allowing the pipe to deform and increase it's contact area on the plate as it does so. This means that the initial stress would be quite high, but then it would peter out as the contact point flattens. I would like to know whether the pipe has yielded in this zone (ie dented the pipe). I would also be interested in whether it was possible for the pipe to buckle in this loading case?
I have looked at table 14.1 on Roarks formulas which kind of describes my loading case, however that is only for a cylinder, not a pipe. I know shell analysis can get quite complex, but I was wondering whether someone had experience on how to calculate such a thing?
Unfortunately I don't have experience using any stress analysis programs otherwise I would just do that :(
RE: Calculating crushing imposed by pipe supports
The Roarks formula indicates a 20mm contact zone due to deformation which seems rather high to me considering the wall thickness is 9.53mm thick (does it to you?), does this mean that the area would have yielded and bent the pipe? Although the stress calculation indicates 1856KPa, this would be after the deformation. I suppose my question is whether or not that 20mm deformation is elastic or permanent (perhaps damaging the coating for galvanised steel) and also whether or not I have to worry about buckling about the pipe wall.
If the loading is 1856Kpa what does that even mean? Surely the buckling load would be a lot less than gross yielding?
Over time, the erosion (cutting) and corrosion in the grooves and scars will cause even greater loss of metal at the touch points. And the touch points are the greatest stress risers since they are at the edges of each support, where the pipe begins sagging back down.
To consider laying a 24" pipe on a concrete "plinth" is nonsensical when considering the miniscule cost of clamp curved supports.
The issue also arises from crevice corrosion and general corrosion on the underside of the pipe which you can't see until it leaks.
see attached if you really want to do some calculations and check it out.
The pipe will be fixed to the support with minimal movement and be wrapped in neoprene to protect from wear due to movement so my only concern regarding this is the loading stress.
Something like this www.aaatech.com/catalogs/pipe-shoes/5020/index.htm
Shoes will be well worth the minimal investment.
As far as your concerns as to deforming the pipe, I suppose it's a possiblity, but I've certainly never seen it happen. It's fairly common practice to support piping on a steel or thermoplastic half round (maybe a half inch across), and I've never seen a failure or even visible deformation from those. Look into that if shoes are too costly...
While I guess I'll let others debate any practical issues of rust etc. of conventional well-shaped and padded vs half-round supports, I think particularly/near infinitely small contact areas along with other common factors inevitably breed higher levels of localized stress, particularly with weak or thin pipes or insulation etc.
With my 600NB pipe I have 1.410KN/m of steel and 2.690KN/m for water.
Depending on the length of the line and therefore the number of supports I can assume that if the spacing is 4m then the reaction at the support shouldn't be much more than 20KN.
Even if the pipe contact is 0.5mm over a 0.5m support the stress is only 80 MPa and as the pipe flexes this would be reduced even further so I don't see any possibility of undesirable deformation.
Regarding the contact loads at the edges of the support rconner mentioned, that calc gives 18.3 MPa for a 90 deg saddle, well below anything even worth worrying about. So I can't really see the stress suddenly jumping to ~300Mpa just because it's sitting on a flat support...
After just googling 'pipework' in google image search it's not that unusual to see pipes sitting on flat plates or flanges so I'm not sure why everyone is convinced i need them...
Regarding corrosion, I don't see how sitting a pipe on a flat plate rather than a seat causes more corrosive conditions if my stresses are still so low.
Everyone on this thread seems so adamant that this is not the thing to do but nothing so far has convinced me. I suspect saddles are only necessary for cross country \ long length lines where you are placing your supports at maximum lengths.
It causes more corrosion because there is a small gap where water gathers and where small movements create erosion of the steel.
Feel free to ignore literally hundreds of years of experience from the posters on this thread and build your system as you want, but it will probably take several years to show you why you're wrong. Not everything can be calculated.
Good luck.
I believe a whole lot of factors may enter into the design of some piping on supports systems, and maybe even some e.g. like seismic, vibration and modal effects etc perhaps not real obvious upfront. While I would not state "adamantly" that flat supports cannot be utilized in this particular application involving pretty good-sized and 3/8 inch thick steel pipes, and who knows may even be desirable for some reason(s), and I for one am not going to "worry" about this, one should however be aware for this or future reference that much higher and perhaps even more variable stress concentrations (in the order of a unit of magnitude or higher) and deformation can result between the results obtained at any shaped saddle and those actually near a flat support.
While there is indeed some record of suitable performance of at least legacy steel and iron piping systems in at least the smaller diameter sizes (with substantial ring and beam stiffness) on essentially “flat” supports, larger diameter pipe systems often involve shaped saddles, cradles, or braced hangers that better distribute various loadings around the bottom portion of the pipe. The exact amount of stress in any particular application is dependent on pipe size, pipe wall thickness, type of determinate or indeterminate support scheme, distance between supports, if and how pipes are strapped down, location of supports along the pipe length, loading (including anything inherent to the system and environment, seismic factors etc) and probably many other factors. Readers of this thread unfortunately don't know as much about all this as the OP.
Though I think some more involved formulas addressing these high stress concentrations for cylindrical shells and pipes based on pure point or line localized loads for lesser support schemes have even been published in some technical literature, I suspect one may find more variability and less confidence in same as pipe sizes get larger. Some designers of steel piping systems may go with shaped supports or related schemes like ring girders and others mentioned on this thread etc in some cases as pipe sizes get larger for greater confidence in results or to optimize span lengths etc (therefore building no more piers or pedestals to than necessary for dependable service, and maybe even minimizing total installed cost, minimizing construction time by building less piers or pedestals, and also minimizing clutter to the facility or landscape in the process?)
All have a good weekend.
I've been reading some of the Australian standards and there's no requirement for seats detailed there but it does say:
It also says this
So that means I have a maximum shear capacity of 150MPa.
If my supports were at the specified 12m spacing I think I would be worried due to the combination of bending stress and shear stress at the corners of a flat support but at 4-5m I'm not.
I would have thought that having a pipe on a flat support would actually provide better ventilation to the contact area compared to a saddle. That coupled with the fact I am using neoprene for vibration dampening and abrasion protection I am just not seeing a corrosion risk that wouldn't be there anyway. That said if my stresses were higher because I was using a longer spacing between my supports then I could definitely see the reasoning behind using a saddle to reduce the contact stress.
I can see where you're coming from, but this requires the concrete supports to be initially built perfectly flat and remain that way for the life of the pipe.
You said earlier "the pipe will be fixed to the support worth minimal movement...." How exactly?
How many supports are there?,
what is the plan view?
Will the concrete peers settle over time?
Why don't you want to make the supports farther apart and use a shoe system?
If it looks justified then maybe it will work, but it doesn't look like at the moment.
Using hertzian stress calculations from Shigley's Mechanical Engineering Design which can be found here http://www.amesweb.info/HertzianContact/HertzianCo... it is possible to find the principal stresses developed by the localised contact stress. These principal stresses can be analysed using mohrs circle and are acting in the y and x direction when looking at a cross section through the pipe. The highest stresses induced from contact are developed a few millimetres higher than the contact zone, however when looking at 3D principal stresses, the flexural stress developed due to the bending moment on the pipe is nearly always critical. When this is considered, the highest stress zone is always a shear that is localised to the very bottom of the pipe, at the edges of the support.
However even if the pipe yields, the pipe will self relieve this stress, so buckling is practically impossible provided the support structure is sensible. Having said that, micro cracks will develop in the yielded pipe and the risk of corrosion becomes quite high.
The contact stresses developed are not only dependent on the material of the pipe, but also the material of the support. It is important to not only check the shear capacity of the pipe, but also the support.
Using a design yield capacity of 138MPa which is appropriate for API 5L Grade A steel typically used in my area, the maximum allowable shear is 0.6 times that (82.8MPa). This is very different to what I thought earlier in this thread as I was still wrapping my head around the problem so bear with me. My calculations are based on the UDL generated from the self weight of pipe and water, with no other components attached to the pipe. I found some typical maximum flat lengths with practical support intervals for use on a steel support. The stress found is shown below.
So for example a support length of only 210mm for 12.8m support lengths of DN600 pipe is actually fine (81.5MPa contact stress). When I switch the support material to concrete the stress on the pipe drops off quite a lot due to the lower elastic modulus of concrete. However, note the stress on the concrete is well in excess of allowable shear stress...
When I make the support into a shoe of 615 ID and return it to a steel support the stresses drop off quite a lot.
When I return it to a concrete support the shear stress noted on support for the DN600 pipe is acceptable due to the 615 ID shaped slot.
So in my mind I think that flat supports are okay if you keep the support interval rather short and an appropriate support length is selected. If using concrete supports then shaping the concrete pedestal into a shoe a few mm larger than the OD of the pipe is desirable to stop the concrete from cracking at the edges. If the pipe lengths are supporting valving or other equipment, or if the pipe configuration is not a typical run of pipe (tee pieces etc) then the moments and reactions of the support must be calculated in order to find the contact stress.
That said, it is always better to use a shoe (as expected), but not always necessary.
Nothing wrong with this conclusion. Starting with an empty pipe resting on a flat floor, the stresses are low.
Them remove parts of the floor and add content weight the stresses go up until the pipe deforms and sags over the remains of the floor.
In practice steel resting on concrete is going to suffer damage from corrosion and/or wear.
If your application happens to involve pressurized piping, as of course many do, you therefore may wish to also consider any additive effects of e.g. hoop stress due to at least very high internal pressure, that are of course also mostly circumferential, also tensile in nature and also located at the inside bottom surface of the piping. [Internal pressure will also tend to "re-round" the piping, reducing the contact area you mention early in this thread, but in so doing perhaps obviating additive effect to maybe some extent.]
You have to keep in mind that the formulas are actually already conservative because they assume a perfectly rounded cylinder.
AFAIK the stress distribution is something like this:
So due to the fact that these are compression forces acting in the same direction to hoop stresses which are tensile forces, an internal pressure actually provides a strengthening quality to contact stresses and can therefore be negated (IMO).
Notice specifically the location and direction of Parmakian's bending moment M, and also "T = tensile stress resultant in pipe shell, positive as shown in Figure 1." Parmakian developed a differential equation via substitution involving five equations with five unknowns involved, and with solution of that equation and further study he concluded "The pipe shell stresses which result at the bottom of the pipe are due almost entirely as a result of the bending moment M."
Again, I am not primarily talking about the "contact" or shear stress, but instead (basically I believe Parmakian's) tensile bending stress at the inside surface of the pipe as a result of the bending moment at that location, and that weight, hoop stress due to eventual filling and internal pressure (not included in Parmakian's model), and maybe even other installation and service loads, might under some conditions be at least some additive to e.g. Parmakian's initial tensile bending stress (as of course hoop stress is also tensile, and also "positive", at the same location as well as elsewhere around the pipe).
While certainly not saying it will occur with your steel pipe and spans, it might be more descriptive to visualize e.g. a non-ductile (brittle) pipe ring say being crushed by loading between two flat plates -- if you are watching the test, I believe you would eventually see (as I believe Parmakian's model predicts) distress or a crack first open up on the inside surface of the pipe or lining very near the (clock) locations of load application.