Cover to pilecap bars over the pile

Cover to pilecap bars over the pile

Cover to pilecap bars over the pile

(OP)
Hi,
From the reference of CRSI Handbook(2008) 75 mm cover was provided between pile cap main re-bar and pile, which makes a cover of 150mm from bottom of pile cap to pile cap main re-bar. There was a difference in opinion regarding the above, as some of believe in placing the pile rebar over the pile.
Two things come into play if the bars are set directly on the pile. First is the partial loss of bar development. How much that can be is unknown since the development length equations in ACI include various amounts of clear cover. If the bar were to rest on the pile, the clear cover would be zero over a length of pile. Therefore, a reduction in effective bar area for pile-cap flexure at the pile location would occur. This would reduce the moment capacity of the cap.
Secondly, if the top of the cutoff pile is above the water table, there may eventually be water infiltration around the pile that would tend to produce corrosion in the bars resting on the pile. This will also reduce effective bar area which will further reduce moment capacity. We cannot predict how much this could be.

Some believe the 150mm cover to pile rebar may crack and corrode the rebar in pile cap when water table is above the pile cap.

Could anybody give proper reference from Aci for cover to pile rebar over pile,and also give the best solution for above mentioned.

RE: Cover to pilecap bars over the pile

(OP)
hi ,
Could any body answer my previous question

RE: Cover to pilecap bars over the pile

The ACI 318-08 code reference is Section 7.7. Since the bars will be exposed to earth or weather, the minimum clear cover is 2 inches. This should be dimensioned from the top of the pile since it is not a continuous pour and water can get in through the joint. If you're worried about corrosion on the bars, you can always specify a deeper cover (this is what is typically done) or use epoxy coated reinforcement. A cover of 3" should be okay for water.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources