Banner Wind Loads

Banner Wind Loads

Banner Wind Loads

(OP)
I have a client that wants to hang a banner from the side of an existing building. The banner is supported at the top and bottom and is 4’ wide x 20’ tall. The code to be used is ASCE7-05. My question is which wind load section on ASCE 7-05 does this fall under? I am guessing section 6.5.15 as the sign is not freestanding.

RE: Banner Wind Loads

I don't see this a sign - a rectangular vertical plate sticking out of or above the ground. I would look at C&C wall loads.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Banner Wind Loads

ASCE 7-10 has a section (29.4.2) on solid attached signs that reverts to C&C loads with the internal pressure coefficient set to 0. Is your sign on or close to the building wall?

RE: Banner Wind Loads

(OP)
JAE,

WOW posting at 12:00 am that's dedication.

azcats

Yes, these will be close to the building, about 4' away to the outer edge max. I didn't get a chance to look at ASCE7-10 to see if there was any clarification. I'm surprised they use C&C loading with the internal pressure set to 0 as I think that would give you lower wind loads.

RE: Banner Wind Loads

Second the above comment, this should use the C&C load for the building in my mind. Probably a lot of engineering judgement involved in using even those loads for this application, though. I imagine that unless this is pulled really tight, any "flapping" of the banner can cause some pretty extreme loads in the banner and its anchorage.

Maine Professional and Structural Engineer
American Concrete Industries
www.americanconcrete.com

RE: Banner Wind Loads

SteelPE - I believe that section only applies to signs 3' or less away from the building face...so the lower loads somewhat make sense.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources