I'm pretty sure there's an easy fix but I just can't figure out how to create the PLC ladder to control three water valves, here's how it should work:
press button to select number 48 valve to go fully open (actuator's only require momentary energising to operate), as soon as it reaches fully open the fully open limit switch on number 48 valve should trigger the number 49 and 50 valve's should go fully shut. Then it's a matter of going the other way, press button to select number 49 and 50 valves to go fully open, the fully open limit switches of each valve should trigger number 1 valve should go fully shut.

Hopefully the drawing should show how I currently have the ladder logic.
The problem is that when I try to drive valve 48 open again, it's being forced closed by number 49+50 fully open limit switches as per the bottom piece of ladder.
Any ideas most welcome

RE: Valve control via PLC

I think you wanted W49 Go Open / W50 Go Open to be outputs. You seemed to have corrected that before on the previous line, and might have missed it below.

If you are using the same push button to do these two processes, then you will need another latch. As it stands when you press the button all three valves will open.

RE: Valve control via PLC

(OP)
Hi ApexMOEng, apologies for such a rough sketch, I've added some additional info to it here:

RE: Valve control via PLC

Use one shots and set and reset coils. For example the series W49 fully open and W50 fully open triggers a one shot. The one shot (which remains active for only one scan) sets the W48 close command. Once W48 is fully shut, reset the W48 close command which will allow W48 to open.

RE: Valve control via PLC

Something like

CODE -->

[PB]--[/LS1]--[PROCESS LATCH]--->(VALVE 1 OPEN)

[LS1]--[PROCESS LATCH]----->(VALVE 2 CLOSE)
                      ----->(VALVE 3 CLOSE)
                      ----->(PROCESS LATCH)(OTU)

[PB]--[/LS2]--[/LS3]--[/PROCESS LATCH]----->(VALVE 2 OPEN)
                                      ----->(VALVE 3 OPEN)

[LS2]--[LS3]--[/PROCESS LATCH]-->(VALVE 1 CLOSE)
                              -->(PROCESS LATCH)(OTL) 

You want to separate your processes somehow, such that they are in distinct states and some variable or latch controls when each can occur.
Or else you run into things where other parts of your code are trying to activate when they shouldn't.
Since ladder logic works as:
Read inputs -> scan code top to bottom -> Update outputs

The need for these control variables is necessary or else output commands will fight eachother.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close