A question about Example 7-1 of CT Trenching and shoring manual
Hi, I am trying to design a braced soldier pile wall with the help of CT manual, but I seem to have problem finding the required depth of embedment of piles. According to the manual I need to take moments about brace location on the pile to calculate embedment depth using a factor of safety of 1.3. Doing that leads to a third degree equation which gives only negative roots for D. I checked the example 7-1 of the manual (page 7-14) and put M_R=1.3M_D on page 7-18 which in turn gave me this equation
D^3+25.66D^2+94.96D+185.71=0
which also gives negative values for D and off coarse totally different from what the manual suggested which is
D^3+18.7D^2-114.53D-223.98=0
I checked the procedure before equation above and they all seem to be right but putting M_R=1.3M_D just doesn't give D^3+18.7D^2-114.53D-223.98=0.
I just wonder if there is something wrong with the procedure suggested by the CT manual or I'm just too stupid to do basic calculation :)
I found a link to mentioned example here (http://files.engineering.com/download.aspx?folder=...)
would you please take a look at page 7-18 and help me with that example. Thanks.
RE: A question about Example 7-1 of CT Trenching and shoring manual