Gounding of an industrial facility

Gounding of an industrial facility

Gounding of an industrial facility

(OP)
In designing a grounding system for an industrial system, I typically focus on all faults that might occur on the secondary side of the main transformer. These are small facilities, less than 3 MVA. The ground grid and rod are sized large enough to carry all fault current, as are equipment grounding conductors. But all of my calculations are based on faults on the secondary. Recently I was questioned about whether or not the ground system could handle faults on the primary. For a small industrial facility without a substation, what is the design engineer's responsibility for faulting on the primary side of the transformer? Of course these cannot be cleared by the facility, but should the utility faults be part of the ground design?

Thanks
EE

RE: Gounding of an industrial facility

In my opinion, 3 MVA represents a big transformer for a low voltage supply system. That means the transformer is close, or even, it is located on the facility ground grid.
In a case of a fault on medium voltage side of such a transformer-usually phase-to-ground-to-phase-the ground grid potential could rise very high. The Utility has to state the fault current level in each such point-it is my opinion.

RE: Gounding of an industrial facility

(OP)
Yes, the transformer is on the facility ground grid, and within the fenced area of the facility. And no, the utility will not reveal the secret fault current. Of course they should, but they don't.

RE: Gounding of an industrial facility

How can you calculate the secondary fault current without knowing the utility source impedance?

RE: Gounding of an industrial facility

I should take the short-circuit apparent power as per IEC 60076-5 Power transformers. Part 5: Ability to withstand short circuit. Table 2 – Short-circuit apparent power of the system.
For up to 24 kV medium voltage system the power indicated it is 500 MVA.
So, the system impedance has to be Zsc=V[kV]^2/500. If no power station is in vicinity X"=Zsc.

RE: Gounding of an industrial facility

The Thevenin equivalent impedance of a system is not a set value and can vary greatly depending on the location (electrically) in the system. You need to either calculate this value yourself via the system base models (using ASPEN or PSS/E) or you need the utility to provide this value at the point of common-coupling.

RE: Gounding of an industrial facility

(OP)
This is not about protecting the transformer. The utility provides that protection. My concern is whether or not it is the design engineer's responsibility to consider faults on the utility side as part of the ground grid.

EE

RE: Gounding of an industrial facility

A failed arrestor on the high side of the transformer is a utility side fault on the ground grid. Seems to me that you should take that into consideration.

RE: Gounding of an industrial facility

The design of a ground grid is based, essentially, on how much current returns back to its source through the earth under fault conditions. Often times (but not always...) primary faults are the basis for the entire design.

RE: Gounding of an industrial facility

(OP)
So how does a facility engineer design a ground grid to protect against a fault he cannot clear and whose magnitude is unknown (unless you consider infinite bus a magnitude)? The goal is to assume that the fault current will return to the source under your facility. Assuming the fault hits a grounded piece of metal, the grid will route the current into the ground, if the fault doesn't melt the copper. What if it a phase falls to the ground and hits dirt? How do you protect against that? What if the dirt is frozen?

EE

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources