Determination of critical compressive stress without K value?
I am attempting to determine the critical stress, Fcr, without using the effective length factor, K. If I read this correctly; section C-E3 of AISC 360-10 states that the limit between elastic and inelastic buckling can be defined as F¬e=0.44*Fy. If this is true than Fe depends on Fy (and vice versa) which then means that (Fy/Fe)=2.25 and Fcr is then forced to be equal to equation E3-2. Where is the mistake in this thinking?
RE: Determination of critical compressive stress without K value?
I'm going to assume that we're talking about the direct analysis method based on some of your recent posting. In that case, the critical stress should be based on KL = 1.0L.
The fact that the limit between elastic and inelastic buckling occurs at Fe=0.44*Fy does not mean that Fe=0.44*Fy. Fe=pi^2*E/(KL/r)^2, same as always. As KootK mentions, for DAM, K=1.0.
Thanks guys. This wasn't related to the DAM, I was checked the critical stress for a HSS column and was wondering if it's possible to avoid calculating K.
Not without some sort of p-delta or deflection based moment magnification or something. Anything you do to avoid assuming or calculating K is going to be significantly more calculation intensive.
TLHS, don't forget about the reduced stiffness.