Horizontal cracks in column under ramp

Horizontal cracks in column under ramp

Horizontal cracks in column under ramp

(OP)
Picture shows horizontal crack runs along the column just under the ramp at 3rd and 4th levels of structure. Still the building is under construction and just completed 4th level slab/ramp concreting. Foundation is a piling system rest on bed rock. Anybody can explain what are the reasons for this please..?

RE: Horizontal cracks in column under ramp

The potato used to take this picture has a pretty poor resolution, I can't even see a crack.

Maine Professional and Structural Engineer
American Concrete Industries
www.americanconcrete.com

RE: Horizontal cracks in column under ramp

I think it's along the horizontal edge of the formwork.

I wouldn't be surprised if it's just bleed water spalling off or something like that. But it's tough to tell on the picture.

RE: Horizontal cracks in column under ramp

Like the others, I don't see a crack.

RE: Horizontal cracks in column under ramp

Still hard to tell if they are cracks or just indicate roughness of the formwork or similar. If they are indeed cracks, the most common causes near the tops of columns are overly exuberant removal of forms, and plastic settlement due to inadequate compaction.

RE: Horizontal cracks in column under ramp

From the first picture the column in general appears to have been vibrated sufficiently, at least for the majority of the height. They may have gotten lazy at the top of the column but that seems unlikely.

Removal of the formwork above the crack would likely aid the discussion.

RE: Horizontal cracks in column under ramp

Difficult to tell from the photos, but looks like it may be a cold joint. Inadequate vibration during placement combined with a time lag between successive layers of concrete being placed in the column/wall. Early removal of forms could have also contributed.

RE: Horizontal cracks in column under ramp

Looks like a cold joint to me

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources