BEAM WEB CRIPPLING
BEAM WEB CRIPPLING
NEED ADVICE ON THE CALCULATIONS TO DETERMINE THE ALLOWABLE CRIPPLING FORCE IN WIDE FLANGE BEAMS.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
RE: BEAM WEB CRIPPLING
That being said, determining the adequacy of a beam for certain loads (and the maximum load acceptable for certain beams) is directly related to the unbraced length of the member and the member's section properties. The easiest way to determine these load limits is to consult the AISC Steel manual (ASD Part 2 or LRFD Part 4, depending on what code you're using). This reference has tables for maximum allowable (or factored) uniform loads for beams laterally supported and charts for beam design moments. If you know the unbraced length of the beam and how to properly read these charts, then the information you seek is simply attained.
If you're not in the U.S., then you need to reference the corresponding code. I'm only familiar with AISC.
Hope this helps!
Matt
At the end of a beam, use: R/[(N + 2.5k)*tw] <= 0.66Fy
At an interior concentrated load, use: P/[(N + 5k)*tw] <= 0.66Fy
Where: N is the length of the bearing on the web;
k & tw are given in AISC manual;