Design Anchorage without Shear or Tension Load?

Design Anchorage without Shear or Tension Load?

Design Anchorage without Shear or Tension Load?

(OP)
Typically I have designed post-installed concrete anchorage for outdoor tanks that are subjected to wind load. With the wind load, I can establish an over-turning moment, and then design for the tension and shear load using ACI 318 Appendix D. When a tank is located indoors on a 4" deep housekeeping pad and is not subjected to a lateral load, how does someone determine the size and frequency of the post-installed concrete anchors? Without a lateral load does any code establish a minimum strength, I didn't find a minimum in ACI 318 appendix D.

RE: Design Anchorage without Shear or Tension Load?

Try the hilti profis software, it's located on their website. Also, I like to design tanks for "oopsies" like a forklift running into it by accident.

RE: Design Anchorage without Shear or Tension Load?

Even indoors, you'll still have seismic loads and 5 psf code mandated wind load. Beyond that, just be glad that it's easy to make the design work! Most engineers will also consider a lateral load of 2-5% of the weight of a structure regardless of environmental load conditions.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Design Anchorage without Shear or Tension Load?

For larger steel storage tanks, they are typically not anchored unless required by the calculations.

RE: Design Anchorage without Shear or Tension Load?

(OP)
Thanks a lot guys, I decided to use the 10% of the vertical load.

RE: Design Anchorage without Shear or Tension Load?

ASCE 7-10 talks about when tanks are allowed to be free standing or friction held. However, we always anchor tanks because it's good practice.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources