Ground Test Well Electrode Connection
Ground Test Well Electrode Connection
(OP)
Hello all.
At ground test wells that are part of a ground ring, is it typical to make the ground ring connection to the electrode in the test well with an exothermic or bolted connection? I understand that bolted connections might be preferred for Fall of Potential testing.
Thanks.
b
At ground test wells that are part of a ground ring, is it typical to make the ground ring connection to the electrode in the test well with an exothermic or bolted connection? I understand that bolted connections might be preferred for Fall of Potential testing.
Thanks.
b






RE: Ground Test Well Electrode Connection
An exothermic or compression connection cannot be easily removed for testing, so why have a test well at every rod? Just put one test well for access to the total grid.