RE: NEC Code Verification
The best answer for the NEC is Art.210.19(A)(1) for branch circuits and Art.215.2(A)(1) for feeders. I had to oversize neutrals many times because of nonlinear loads and harmonics. There is special transformers called "K Type" that have up to 200% larger neutral windings.
Hope this helps,
Dave