welding 25M rebar to steel plate.

welding 25M rebar to steel plate.

welding 25M rebar to steel plate.

(OP)
How is the weld of a 1" diameter rebar to the top flat surface of a steel plate designed and specified? Want to transfer a factored force of 40 kips. I expect that about 3" length of 5/16" fillet weld each side of the bar to the top surface of the plate below would be sufficient.

RE: welding 25M rebar to steel plate.

I always refer to a handy table in the PCI manual that deals with exactly this. I assume that it's vetted to some degree. Some things to consider, many of which are probably obvious:

1) Weldable rebar.
2) Welder qualified for the work.
3) It's a flare bevel so size is pretty much a function of radius.
4) It's a flare bevel and effective throat is questionable in my opinion. A little conservatism on the determination of weld length is appropriate.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: welding 25M rebar to steel plate.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: welding 25M rebar to steel plate.

(OP)
To Kootk - perfect. That is exactly what I was looking for. Thank you very much.

Andy

RE: welding 25M rebar to steel plate.

(OP)
I am trying to check this table to make sure I understand it.
Is the intent that if the tabulated length of weld is provided, then it will develop phi fy As = 0.90 x 60 ksi x As?

What does 0.2 dbmean?Is that the effective weld size?

What material factor (phi) is incorporated for the weld?

How do the E70, E80 electrodes etc., compare with the metric electrodes listed in the Canadian Institute of Steel Construction (which are E410XX, E480XX, etc)?

For the case of the bar-to-bar splice (last column in the table), is it designed for 1.25 times fy As like for mechanical splicesof rebar?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources