Can anyone help me regarding BBP open circuit logic or algorithm in details.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Bus bar differential protection Oct logic
|
RE: Bus bar differential protection Oct logic
I'm just going to assume when you say open circuit logic, that you are referring to open CT detection.
In a normal Bus Differential scheme without the use of open CT detection logic, if one were to lift a CT wire or if a CT wire were to come out of a lug.......etc, the Bus differential would operate and clear the bus right. Well Open CT detection logic allows the relay to distinguish an actual differential and trip on a fault with in the zone or to remain in service and alarm on an open CT.
Here is how it works:
When the CT circuit opens up, there is a spike or increase in "operating current" and a corresponding dip or decrease of the same magnitude in "restraint current" The increase in operate current and decrease in restraint current should sum to zero. Every relay is a little different but essentially the relay is saying "Is the operate current above X per unit? Is the restraint current below X per unit? Is the vector Sum of restraint and operate current very small (close to 0 zero)? If so, I declare an Open CT"