Cantilevered Decks and Balconies
When you compare Table 2 from the DCA6 to a similar Table (R502.3.3(2))in the 2012 IRC for cantilever spans for floor joists supporting exterior balconies there is a huge discrepancy.
For a 2x10 floor joist @ 24" o/c spacing I can construct a cantilevered balcony per the IRC with cantilever span of 43" and a backspan with a 2:1 ratio.
Using the same 2x10 deck joist @ 24" o/c spacing I can only create a cantilever of 2'-9" and the backspan must be a 4:1 ratio per the AWC DCA6 document.
Why is the AWC DCA6 so conservative? I must be missing something here. I've attached a quick calculation for this scenario and with a 220 lbs point load I'm well below capacity of the joist in bending or any other parameters.
A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com
RE: Cantilevered Decks and Balconies
Mike McCann, PE, SE (WA)
Also, could it be the incising factor based on the AWC assuming treated wood?
You using same Cd factors? Tables may be assuming different values. I don't have AWC DCA6, just brainstorming.
www.medeek.com