Line tripping on transformer inrush

Line tripping on transformer inrush

Line tripping on transformer inrush

(OP)
Is there anyway to get around a line with 9 or so transformers from tripping out on inrush? I know that you have to hit it just right for it happen so it is kind of a rare bird. Do some people use harmonic restraint, time overcurrent curves, or just a delay to give the inrush a chance to decay some before making a decision as to whether to trip out or not? The inrush is tripping out phase distance protection.

RE: Line tripping on transformer inrush

I don't think phase distance protection usually has a harmonic restraint setting. It can however have a time delay setting. Do you have a oneline or a sketch of this system? You have 1 line with 9 transformers fed from it. Is the distance relay protecting the line or the transformers? Which direction is it facing?

RE: Line tripping on transformer inrush

(OP)
No, our distance relaying doesn't have harmonic restraint but I was thinking that something like that could be used because you see it in transformer protection relays. The line tripped on reclosing on a long forward looking zone that was long enough to see the inrush.

RE: Line tripping on transformer inrush

Possibly shorten the zone 1 distance zone so it falls short of the transformers and add a zhone 2 distance zone with a time delay longer than the inrush?

RE: Line tripping on transformer inrush

Quote (JG2828)

No, our distance relaying doesn't have harmonic restraint but I was thinking that something like that could be used
Call and sell that to the SEL/Basler/GE development teams. atom


Do you have a magnitude/time estimate for the transient during reclose? What does the TCC for the relay look like and how adjustable is it?

RE: Line tripping on transformer inrush

Some distance protection are available with inrush restraint ( e.g. http://www.schneider-electric.com/download/ww/en/r...).

That being said, is it the inrush itself causing the maloperation ? Did you check if the CT goes onto saturation ( due to long DC decay) ?
Can this be the root cause ?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources