Trusses with Plywood Gusset Plates
thread337-18639: Ply gussets in wood truss
I'm now about to embark on the wood gusset stage of my truss designer. I've been reading and searching the internet for as many resources as I can in relation to how to best fasten these plates to the truss members.
As a given I will probably spec. out a glue (ie. LNP-902) which I will not consider in the strength calculations to give an additional level of redundancy and margin to the design.
Looking through a number of documents I've seen clinched 3" nails, and unclinched 6d, 8d and 10d nails used. I've even seen some mention of Simpson SDS screws as well as drywall screws. Most of these documents are 50 years old or older so not a lot of recent data on this topic or so it would seem.
I am curious if anyone has any recent experience with using plywood or osb gusset plates on wood trusses and what was their fastener of choice and why?
I really like the idea of 3" nails that are clinched (less nails = less labor) however would a smaller diameter nail be less prone to splitting the wood members even though there are more of them and they are spaced more closely together?
I'm also considering ringshank nails since the cyclic loading on a truss might have a tendency to back the nails out over time, however the shear strength of these nails is a question needing further investigation.
For the actual gusset plate material I'm considering 1/2" DF Structural I Plywood, however I would also like to have 3/4" PLY, 19/32" PLY and 7/16" OSB as additional options. I've actually see 7/16" OSB used in a lot of home built trusses and I'm actually guilty myself of my own home brewed trusses for a small storage shed using drywall screws and 7/16" OSB (8 ft. span). Other than the strength design values are there any other caveats to using OSB in this application?
A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com
RE: Trusses with Plywood Gusset Plates
http://www.public.iastate.edu/~mwps_dis/mwps_web/t...
www.medeek.com
B.E.
You are judged not by what you know, but by what you can do.
The few spreadsheets i made (not nearly as nice as yours!) i have used double shear nails, glue to keep wood from splitting, 15/32 & 19/32 structural rated sheathing and specify the strength axis or design based only on the weak direction (conservative)
Few things to consider is the geometry capacity of the gusset in tension/compression, and geometrically how many nails you can get into it. I usually make sure that my plywood can handle 100% of the load transfer at about 66% of my nails. Since each nail transfers 100#, i want my gusset to handle 133# from each nail (numbers are made up). Geometrically this is really only an issue in tight corners like Top-Btm Chord connections.
I really like the idea of clinched nails and I think that is the direction I will go. Determining the number of nails to use seems pretty straightforward however I'm a little bit conflicted right now as to how best consider the tension and shear strength of the plywood. In some cases the joint line of the plywood is not perpendicular or parallel to the applied load. In these cases would it be appropriate to use the Hankinson Formula (NDS 2012, Appendix J) combining the shear strength and tensile capacity of the plywood?
www.medeek.com
It took about 4 days to cut all the pieces, and 3 or 4 days to assemble all 17 trusses. Make sure you have a nail gun, trying to hammer all those nails will kill you! My gun quit about half way through, and I had to wait a couple days for a rebuild kit to get it up and running again.
I'm curious as to the grade spec'ed out for the plywood gussets.
With a 2-1/2" 8d nail you would theoretically penetrate through one gusset plate and then also through the 2x truss member with about 1/2" sticking out the backside. I'm assuming you had a gusset plate each side though so if you nailed it with both gussets plates in place you should be able to nail the nails pretty much straight.
Did they provide you with a nailing template or pattern or any specific guidelines regarding edge spacing and end spacing?
www.medeek.com
I'll have to look if they specified anything other than 1/2 CDX for the plywood. I don't think so. With the first side, I drove the nails on a slight angle so the end wouldn't stick all the way through. The 8D collated nails are only 2 3/8, not 2 1/2 so with a 2X @ 1 5/8 and a 1/2 plywood gusset, that's only about 1/4" long, easy to fix that with a slight angle.
There was no nailing template per say, just a note for 2" on center with 1" edge distance. On the 2X6s I set then in a square pattern, and on the 2X4s I did a diamond pattern. My nail patterns weren't what you would call precision, just what looked about right as I hammered away with the nail gun. The inspector didn't even really look at the nail spacing when he did the rough inspection.
The floor trusses they were more particular about. The company that built them provided drawings with a PE stamp.
I'm still working on the algorithm for the design of the gusset plates. My process so far goes something like this:
1.) Consider all load cases.
2.) Calculate worst case loads for each member
3.) Design members per TPI 1-2007 or 1-2014 (this part is already well defined within the truss calculator).
4.) Choose a nail size, then determine its capacity (per nail) depending on gusset material, gusset thickness and member material and single or double shear. Load duration factor comes into play here.
5.) Given the lateral loads on the fasteners via the truss members determine the number of fasteners into each member at each gusset plate/member interface.
6.) Determine a min. spacing, edge and end distance for the fastener size.
7.) Based on step 6 and step 5, and with the width of the truss member (top chord, bottom chord, web) determine the number of fastener rows possible and the required length of the gusset plate along the member to accommodate the number of fasteners. This will determine the min. size of the gusset plate based on fastener lateral capacity.
8.) Given the size of the gusset plate determined in step 7 check the tensile/shear strength of the gusset plate material. If capacity is too low increase size of gusset plate.
One item that is also undetermined at the moment is how to best deal with chord splices, especially bottom chord splices that are in tension and bending.
www.medeek.com
1) combine all fasteners and calculate the combined effect (Ix, Iy) and then apply the moment to group and axial and shear. The resultant is then used to find the governing fastener. Easy for spreadsheet that calculates force per nail. This is accurate but tricky to code... ive only done it by hand. I have wished to turn it into excel and possibly treat it by user entered number of rows. Ie 2 rows of 2 per row gives X capcity = NG. User increases to 7 rows of two fasteners per row.... Or a For/While loop?
2) the outer nails on each end of the chord splice handle moment, the middle ones handle axial and shear. So each side of splice gets 7 rows of 2 nails. row 1 and 7 create force couple to transfer moment (spaced 6*2"=12") and the middle 10 nails handle axial....
Your question on when the force is not aligned with a major/minor axis, I think the value for intermediate angles is basked on Hankinson-Formula... i may be thinking of something else so don't trust me :)
www.medeek.com
I've actually done this sort of thing with a spreadsheet for a similar situation with portal frames and the moment capacity of the fasteners so I guess I had the answer all along but didn't even realize it.
See this thread:
http://www.eng-tips.com/viewthread.cfm?qid=374730
The next big question is how to check the tensile capacity of the bottom chord splice (with moment applied) in regards to the strength of the plywood gusset plates. Section 8.7 from the TPI 1-2007 has an equation for dealing with this exact situation for steel plates I am wondering if it can be modified and adopted for wood gusset plates, the basic principles should be the same.
www.medeek.com
Very cool, thank-you for sharing that. I imagine those would have been quite fun to assemble. I'm assuming you probably built some sort of jig so that they all came out the same size and shape with all of those angles and lengths.
My guess is you've enclosed them in gypsum so they are not available for inspection but I wonder how the fasteners and glue are holding up long term and if there has been any significant creep.
www.medeek.com
I will say that the chord splices i have done have always been out of nominal wood, not plywood. So you will have the same moment+shear+axial worry in the chord splices.
As for the calculation of them, i would lean towards a unity of the forces/capacity < 1.0.... However, it starts to get important with the number of plys and such when doing tension/shear/bending about the laminated layers. I usually design the panel points as M=0 for this reason. if my members can transfer all the force as a pin then i only have to worry about the axial and shear capacity. And that there is a table for in the NDS or one of the supplements.
I work in the modular housing industry and our roofs are usually a combination of pre-engineered wood trusses (mitek, etc.), factory built rafter systems and plain old simple framing with a ridge beam. We use gusset plates all of the time. OSB and plywood. The rafter systems are similar to designed trusses, but since the roofs have to be hinged down for transport, we require gusset plates at the heels after the roof is extended on site, then install a knee wall and/or collar ties. (The truss manufacturers have a special steel hinge they use that negates the requirement for gussets). My biggest issue is not the design of the gusset itself, but getting to correct design loads. After that it is pretty straightforward to design the gusset. In my experience the fasteners control the design almost all of the time.
Beyond that, a thought about nails sizes.....although still used, hand hammered nails of the 16d, 10d, etc. variety of nails have been replaced with pneumatic nail guns. The are a myriad of options for these guns....and are usually specified by diameter and length, e.g. 0.131 X 3" nail. That is actually a longer 8d nail. As I said, you can get almost any combination of diameter vs length. Check your local lowes or Home Depot, or check out Senco and bostitch nails on their websites.
Again I am very interested in this truss calculator you speak of. I would really like to find a simpler, more streamlined calc as opposed to RISA, STAAD, etc.
You had mentioned you wanted to use the clinching technique to save money....not sure how having to,go back to each nail and clinch the tail is time efficient. Especially with the relative low cost of materials (nails) vs labor.
The truss calculator is something I have been slowly working on the last couple of years. It still has a long ways to go before it is really a useful piece of software, the problem of course is finding the time to spend any meaningful time to work on it. I started it due to my frustration with the truss plate manufacturers not offering their software to engineers and architects. The current calculator is located here:
http://design.medeek.com/calculator/calculator.pl
It is free to use but I have limited its daily usage to help curb some overuse and bandwidth problems I was having.
What do you typically see in your line of work as the most frequently used nail size for gusset plates? Also do you use glue in combo with the nails?
www.medeek.com
I generally use 0.131 X 2 1/2" or 3" nails. It depends on what the factory / contractor already has in his nail guns. 0.131 nails are ubiquitous in the factory built structures industry and most factories and set crews have this size nail gun. I don't worry about the 1/2" of nail that sticks out. I always use 2 gussets of at least 7/16" OSB or 1/2" plywood, and alternate the required nails on each side of the connection. I do not use glue at the heel gusset because the top chord of the rafter has to rotate down for shipment of the units. There is usually a bolt placed to allow for the rotation, but it is not included in the final gusset fastening calcs. In a static situation I would use 80% coverage of PVA glue on the connected planes.
BTW, I too am frustrated by the fact that metal truss plate companies don't let us regular engineers use their software....I have talked to reps (as high as VPs) from Mitek and Simpson and told them I would specify their connectors if I could use the software. No go at this point. I design more than 100 houses a year which would equate to many, many trusses, but because of the proprietary software I am not able to spec mitek or Simpson plates and use gussets and other direct framing methods instead....loss for them. I keep trying and maybe I can wear them down.
I have used some of your tools from your website and find them very helpful. Thanks for sharing, they are a great time saver for finding the correct design loads.
Thanks again, it is nice to "meet" the designer!
I've been designing wood structures for about 20 years now, that is 95% of my work. Let me know if I can help, or if we can just spitball some ideas back and forth.
Rock on.
Speaking of tools the best single program/tool I've found so far is the Forte app by Weyerhauser. The only major downside I've found with it is the inability to specify wet and pressure treated lumber. Once I realized the load transfer feature was there and figured out how to use it, it has been very handy and saved me a lot of time that I would have wasted manually transfering loads between members.
I'm glad to hear that someone is finding these tools useful. All of them were started at some point or another when I was working on a residential project and fatigue from doing too many manual calcs made me realize there was a better way. Unfortunately, with the Excel spreadsheet tools I have no idea how much they are actually being used.
I've had a lot of interest in this truss designer lately and I would really like to put some more time at it. I actually don't think it will be too much of leap to make it handle the wood gusset plates as it does the metal plates. I'm still undecided on the exact details of how to handle the tensile/shear check of the gussets when the load is not perpendicular or parallel to the "tear line". As you can see in the diagram above the gusset plate is tearing in tension and in shear (approx. 45 deg. angle). The Hankinson formula seems like the best way to handle this.
www.medeek.com
Nails are cheap, labor isn't, splitting my truss is even more expensive! :)
One 26 x 30' garage had a large truss built to go from front to back down the center to carry conventional rafters. That also designed to carry the attic loadings for storage of lumber up there. As I recall the gussets were 3/4" plywood, but bolted at the ends. Some douibling up of members also. No problems at all with any of these, including one house. Full Wisconsin snow loads.
Size of nails and were they in single or double shear (clinched). Glue?
Did you do the calcs on them or did you have another structural engineer run the numbers or did you utilize a more prescriptive approach with span tables etc...
www.medeek.com
It has been a long time since most of this, but for the usual 1/2" plywood gussets, the ring-shank nails were just long enough to come out the other side of the 2 x, so other side had to have its nails also. All the scoop on nail capacity came from the US Forest Products publications. I usually staggered all nailing so that they did not tend to split the member.
The one book I still have here is dated 1974, called "Wood handbook", which I recall was free. US Dept of Agricultural Handbook Number 72.a little over one inch thick pages, in a hard cover.
Library of Congress Catalog Card.No. 73-633335
Try thus link. I think this is it, later version.
http://www.fpl.fs.fed.us/documnts/fplgtr/fpl_gtr19...
One of the buildings (a tractor and wood shed) had the end truss built so the usual end was used as a support for a beam carrying trusses for the next group in over an entry opening of about 10 feet or so. That end truss cantilevered over an opening of about 4 feet. Reason was this building was parallel and next to a driveway, both on a ridge, so right angle or end entry was not possible. I had to drive in under the corner. Of course the end truss was beefed up accordingly. I don't recall the details. I do recall however that the hanger for the beam along the eaves was two galvanized straps, about 1" x 1/8" salvaged from a old windmill, shaped like a "U" also wrapped around that end truss. Can't recall the detail for the connection, but it probably was a series of nails, at allowable stresses.