(OP)
Hi folks,

Please, what is the usual practice for the ANSI 51 pick up for 4.16kV industrial (radial) feeders ?

I have read people saying from 10% to 600% of the ampacity, a bit confusing,

Thanks a lot,

Mongao

RE: MV feeders - ANSI 51 pick up ?

More than the maximum load current, less than the minimum fault current; and coordinated with the upstream devices. There is no numeric rule of thumb that will always meet those conditions; that's why we have Protection Engineers practicing the "Art and Science of Protection". Not just a science.

RE: MV feeders - ANSI 51 pick up ?

Nice reminder davidbeach.

Mongao,
Another issues you have to look at is that it will not be easy to coordinate fuse at the primary of your transformer with the MV feeder circuit breaker.

Common practice for the pick-up setting of the 51 phase overcurrent relay for radial feeder should be approximately 1.3 times the full load current of the 4.16kV MV feeder.

RE: MV feeders - ANSI 51 pick up ?

@leur2011,
Correct. It's not easy but it's done more often than not (fuse protection on primary and circuit breaker on the MV side. You just have to know the published fuse characteristics.

RE: MV feeders - ANSI 51 pick up ?

(OP)
Hi all,

Thanks for helping !

Page 16 of this presentation

http://www.hv-eng.com/OvercurrentProtectionAnnex.p...

refers to NEC 240-100, that mentions that ANSI 51 can be anywhere between 100 and 600% ! It seems too high; but the PDF states that "the intent is to provide protection for overcurrent, not overload". I have used between 20% and 70% in my project, I hope it's OK,

What do you guys think ?

Thanks a lot, I really appreciate it !

RE: MV feeders - ANSI 51 pick up ?

Why would you set at less than 100%?

RE: MV feeders - ANSI 51 pick up ?

(OP)
I should have written between 120% and 170%, sorry,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources