Philosophical Hip Roof Question
I am engineering a 38'x50' house with a standard 7:12 hip roof.
If I can keep all of the rafters from spreading by using the attic floor diaphragm, do the hips need to be designed as beams and do they need vertical support at the peak?
The hips are approximately 27' long in plan and the roof will be sheathed in 7/16" OSB.
The IRC requires the hips to be designed as beams if the pitch is less than 3:12 but also requires them to be supported at the peak regardless of the pitch - which does not make much sense if they are not considering them beams.
RE: Philosophical Hip Roof Question
I vote no on both counts, philosophically. With a rectangular roof plan, however, you will be depending on the diaphragm for gravity load imbalance and gravity load stability in the longitudinal direction. That, in addition to your usual lateral loads.
They usually put in temp. supports. I would design the hips to not deflect too much under the dead load.
FWIW, in the thousands of house I have inspected, I only rarely see issues with hip roofs - usually older homes with low slopes and cut up with spliced hips and valleys.
Mike McCann, PE, SE (WA)
I don't understand your response.
thanks
Just to make sure I am clear - you agree that they do not need to be supported and they do not need to be designed as beams?
I believe that you'll develop a fair bit of axial load in your ridge beams. How you'll estimate that load, design the ridge beams for it, and deliver it to supporting members are all interesting questions.
Lets say your ceiling joists run in the transverse direction and are not turned at the ends of the diaphragm. The rafters framing parallel with the rafters are no problem as you have triangular trusses. For the rafters framing perpendicular to the CJ's you must develop the outward thrust into the attic diaphragm. This would require some sort of strapping from the rafter into the diaphragm. Now the question is how far into the diaphragm must you go? If it were a collector in your LFRS, it would need to extend between chords (which in this case would be your CJ's). This depth would then define your "transfer diaphragm" which would transfer this force to the shear walls on the exterior of the building.
Another likely load path working beyond the ridge (as you move down the hip) is the CJ acting as a collar tie (tension member), then the short piece of rafter being in compression then you have "sheathing strips" in compression along the hip side of the roof.
I have used the technique mentioned by Mike in the past but then the hip would still be designed as a beam as it is spanning from wall to truss.
Maybe there is a better way though?
EIT
www.HowToEngineer.com
You bring up some good points. What I normally do is put a double ceiling joist 4' from the edge and then ladder frame from there. That way all rafters get a ceiling joist lap and all the ceiling joists are tied to the diaphragm. I ended up sizing the hips for the dead load and 10 psf live load and added a post at each peak as I had stacked load bearing walls below that area anyway in the lower stories. On a smaller roof, I probably would not have added the posts.
I agree that the ladder framing is the way to go. However you still have some transverse rafters that would then need to be 'strapped and blocked' into the diaphragm.
I think in reality the diaphragm sheathing can take a fair bit of tension but this is not allowed by code (NDS) or atleast not for diaphragm design. Which makes me wonder - If you were to apply general analysis principles/standards to the prescriptive IRC designs, would you need to assume that the floor sheathing takes tension load? (I don't mean to side track here, I'd have to do some major research into this).
I always dislike the case where in reality it is probably OK, but proving this is just not worth the effort. I suppose this is one of these cases.
EIT