Pavements Drainage Layer
Hi, for flexible and rigid pavements what could be the main reasons to install a drainage layer? My project is located at a non-frost area, with the water table very deep (at GL-15m). Storm intensity is 142 mm/hr for 10-year design period. Traffic is low and at a low velocity (for aircraft and ground vehicles), so pumping may be low. I am thinking that my base (150 mm) can serve as a drainage layer as well. My main question is what are the parameters that determine the use of a drainage layer. Thanks !!
RE: Pavements Drainage Layer
Any time the base has the potential to be saturated and lose stability, even for short periods, drainage is necessary.
Ron, thanks for the comment. My base is 150 mm GW compacted to 100% modified proctor which I will try to use as a drainage layer also. My subgrade has very low permiability. I will check if the base course can act also as a drainage layer... Hope it can. Thanks again.
Okiryu....I would not depend on the base course to be a drainage layer. The drainage layer should be somewhat lower than the base course, preferably by several feet.
Might I suggest that you find a copy of Cedergren's book on "Seepage, Drainage and Flow Nets". He has an excellent chapter on road drainage. At that compaction level and if your "GW" material has 5 to 7% fines (I am assuming it is a well graded material and is likely crushed rock) you might find out that it has a very low coefficient of permeability (you might like to run a test on it to prove that it really isn't "permeable") . I once saw water ponding on a well graded crushed rock Road base material to be placed under a paper machine - and it sat thee for 3 days before it disappeared.
Hi Ron, BigH, as always, thanks for your advice. While I am looking for Cedergreen's book, my base has a permeability coefficient of approx. 2.5 x 10^-3 m/s which I was considering as a permeable material. At least, my USACE manual for pavement design shows drainage layers considered as "Rapid Drainage Material" (RDM) with k values of 3.5 x 10^-3 m/s. Since my base material was close to the USACE value, I was thinking that the base could be used also as drainage layer.
Anyway, I will double check my numbers. The existing pavement that I have to replace does not present signs of drainage problems and it used similar base course as it is a standard material here in Japan. I still have to do more field investigations to check if it has a drainage layer but I think it does not have it as I did not noted any daylight outlet along the pavement (The subgrade has very low permeability so if there is a drainage layer (open grade material layer), I think that it should be a daylight outlet).
Thanks again !!
if you provide adequate cross slope, keep the joints sealed and provide good cross drainage, keeping the 10-year or maybe 25-year, high water level below the level of the aggregate base, than I would tend to agree that a granular drainage layer is questionable
cvg thanks for your comments. I was going to ask about the rainfall design period. Do you normally use 10-year or 25-year? The USACE manual for pavement design calls for 2-year rainfall. Anyway, will check for 10 and 25-years as well..
return interval for pavement drainage varies by agency and region. most US DOT's use 10-year, FAA has long used 5-year, one local city uses 2-year. These generally limit the spread to one lane wide. For critical facilities, makes sense to go higher, maybe 25-year. probably should look at 50-year cross drainage