Conduit Pipe within a Concrete Tilt Wall

Conduit Pipe within a Concrete Tilt Wall

Conduit Pipe within a Concrete Tilt Wall

(OP)
I have a 10.5" concrete tilt-up wall with 2 layers of reinforcing (1 layer each face). I have an electrical sub who wants to run 1" diameter conduit between the layers of reinforcing, tied to the inside of one of the layers. A couple runs here and there seams reasonable not to effect the wall much but in one of the panels they want to run a bundle of like 25 in a single layer about 5'-0" wide. I've thought about designing it as and opening with reinforcing each side, top and bottom. Anyone done this before or have any thoughts?

RE: Conduit Pipe within a Concrete Tilt Wall

I'd enforce limits similar to runs inside of floor slabs. 3" center to center between each 1" conduit and some multiple of the aggregate size. That only makes it 6.25 ft wide. I'd also keep it away from rebar anchorage zones and laps or adjust the lap lengths to compensate.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Conduit Pipe within a Concrete Tilt Wall

Quote (wallerdf)

they want to run a bundle of like 25 in a single layer about 5'-0" wide

That is unreasonable. They are just seeing what they *can* get away with.

"It is imperative Cunth doesn't get his hands on those codes."

RE: Conduit Pipe within a Concrete Tilt Wall

Can you see if they can do equivalent area, and less conduits? 25 1" is like 3 3" conduits, which can be spaced equally apart.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources