Continuous beam on girder instead of column
The reactions for continuous beam on column at middle with 2 point loads at midspan at either side has the following formula:
reactions at column or middle = 11P/16 where P is the point load at either side
reactions at either end = 5P/16
how about if a girder instead of column intersects the middle of the continuous beam (imagine forming a cross).. would the reactions be the same?
RE: Continuous beam on girder instead of column
Mike McCann, PE, SE (WA)
by the way.. were you referring to the outer supports of the girder or outer supports of the continuous beam crossing it? i'm interested in the end reactions of the continuous beam (not the girder) compare to the middle reaction and wondering if it would still be 11P/16 and 5P/16.. can you imagine what I was asking?
No, it would be twice that value, there are two point loads (2P) carried by the 3 supports:
Reactions at column or middle = 22P/16 where P is the point load at either side
If girder deflection at point of contact = 0, then reaction at either side = 5P/16
If girder deflection at point of contact is greater than 0, then reaction at either side is greater than 5P/16, up to a maximum value of P (when the girder is so "weak" that it would deflect with "zero" load). The "continuous beam" just became a simple span.
www.SlideRuleEra.net
www.VacuumTubeEra.net
A procedure for calculating the reaction has been outlined in previous posts. It would be easy to set up on a spreadsheet.
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
If not, open your Hibbeler structural analysis book and pound away at an energy method.
"It is imperative Cunth doesn't get his hands on those codes."
Yessir. If the girder is properly designed to support the continuous beam, I suspect that the impact of its flexibility will be relatively small.
So if your girder is big.. it would attract more weight to it than if it is less big.. so is it logical to design it not big so that the other beams at the ends of the continuous beams would share some load?
That's wrong Slideruleera. Look at the following from www.awc.org/pdf/DA6-BeamFormulas.pdf
Want a certain size continuous beam to support maximum load? Design a "strong" girder.
Want to distribute the 2P load equally at four supports (at both ends of the continuous beam and at both ends of the girder)?
Design an optimal sized girder to do exactly that.
There are many possibilities, no "correct" answer for all cases.
Exactly what I said.
Seriously, this is how we are designing Navy stuff now.
Did you notice that when your make the flexure of the girder stronger, it can attract more load and hence more shear in the girder?? What is this design principle called where you have to adjust between flexure and shear counterbalance.. because the less flexural capability, the less load and less shear at the support.. do designers think of this?
Yes.. I usually solve for 11P/16 for one side first and multiply by 2 since there are 2 sides.
Hi wilbers, I think what you are pertaning to is the effects of stiffness/rigity of members to the load distribution in a system. This phenomenon is largely expalined to civil engineering students in the theory of structures courses.
However, a good analogy is when you have a piece of log carried by 3 people, the strongest of the group will carry the largest load but it is still dependent on where he is in the system and how "weak" the others are. The closer he is to the center of mass the more loads he will be carrying.
A well experienced structural engineer will always be aware of this and take this into consideration when setting out the framing system.
This all assumes the continuous beams end are at same level as the girder.. but during construction if the girder is higher by let's say 10mm.. then the ends of the continuous beam will always be 5P/16.. is this agreed by all here?
Note also that you usually put the top bars of the continuous beam over the girder bars.. this means the continuous beams are always higher than the girder..
Kootk.. is it like during concrete pouring.. the initial formula 5P/16 at the ends of the continuous beam got reset. And upon removal of the formwork even if the girder is one meter higher, the deflections from formworks removal would redistribute the moments and make the ends contribution higher. Is this what you meant? I can imagine the spring analogy of girder flexibility but can't see how it could still work even if the girder or spring is one meter higher... do you have other ways to explain it? thanks..
The formwork business complicates the important features of this unnecessarily. I'd recommend just envisioning a pair of steel beams.
Try looking at it through the lens of superposition:
1) Take the interior support away from the continuous beam altogether. Your end reactions would each be P.
2) Add an upwards force (R_c) at the center of the continuous beam of any magnitude. For statics to be satisfied, the end reactions must become P - R_c/2. This is valid for any center support reaction that might be rigid or flexible, such as the support provided by a girder.
3) For the particular case where the interior support is rigid, R_c would be the force that would return the center of the beam to an elevation level with its ends. End reaction = P - R_c/2 = 5/16P.
If you apply this logic to any of the cases that we've been considering, you will find that it holds true.
I got the above.. but there is something else. remember the ends of the continuous beams are on other beams and the beam can deflect too. I tried to imagine this scenario while sleeping and it keeps me awake half of time. So let me ask about this to be certain.. what is the effect if the ends of the continuous beams deflect too via the beams carrying the ends??
Why not have a play with some computer analysis, and you can check the results tie in with your intuition, or if they don't you can investigate why not.
I have a free continuous beam analysis spreadsheet which allows spring supports or defined deflections at the support, and can be set up very quickly:
https://newtonexcelbach.wordpress.com/2015/04/03/conbeamu-update-defined-support-deflections/
Doug Jenkins
2) if an end deflects upwards, it will increase the reaction at that end, decrease the reaction in the middle, and increase the reaction at the opposite end.
3) if both ends and the middle support deflect the same amount, you're back to 5P/16 & 11P/8.
Also, what you can do is dust off your physics textbook and play around with the basic equations for springs in series and in parallel. Then you can relate that back to your "real" system of flexural and axial "springs".
When I model it in Etabs.. the girder (either side) is coming out with 0.54P and continuous beam end at 0.454P. While the formula is 0.68P for girder and 0.3125P for ends. How accurate in Etabs in this thing?
Only as good as the input!
Did anyone notice that in continuous beams.. if the girder near the face of column got cut off suddenly (say from shear failure), the continuous beam ends from both sides can still carry the entire loads even temporarily enough for the occupants to run outside. Has anyone thought of this in the design? Me and my colleagues don't think usually of this.. like if one member fails.. how others would take over.. do you usually consider this in your design?
You are right Ingenuity. Anyway just this one question about etabs and continuous beams.. when modelling the continuous beam ends.. must you initiate Moment Release there or not?
This type of analysis is called progressive collapse and it used quite frequently, especially in highly sensitive buildings.
If you release the moments, the beam is not continuous.
No. If you don't release the moments in etabs in columns based continuous beams the following results (it's not clear if you need to release the continuous beams when it is BEAMS crossing BEAMS, well?)
from http://www.academia.edu/10032492/How_to_Model_and_...
Releasing the moment at the interior supports will make the beam non-continuous. The definition of a moment release is exactly as it sounds, it releases the moment. This is why people should not blindly follow design guides without knowing what the guide itself is doing. By the looks of it, it's not even a good design guide. Beam fixity is a basic concept of structural engineering.
If the edge is moment connected to the column with many bars.. or in other words.. not pinned but fixed connection.. can this affect the formula of 11P/16 and 5P/16?
This is what is puzzling.. in Etabs why do you have to release the moments at the edge when in actual contruction, the edge can even be fixed and 5P/16 still satisfies as the earlier messages by Kootk and company shows?
Which message are you talking about?
The 5P/16 factor only applies for pinned supports with no deflection at any of the supports, and no moment restraint. Any change from those conditions will change the reaction distribution.
Doug Jenkins
Thanks for this important information. Before some structural engineers told me in continuous beams where the middle and ends support are columns.. they just assume it's pinned (since it's so difficult to tell how many percentage is the column-beam connections fixed or pinned). So what they did is put few moment bars in the ends assuming the middle column will take the major loads (close to 22P/16). Anyway. In your designs guys.. how many percentage do you think is your column-beam pinned or fixed? Do you design it as pinned or fixed?
You bet. Fixed end connections will draw more load to those ends.
You don't have to release the ends of continuous beams. In fact, for most monolithic beam/column/girder framing systems, I'recommend against doing so. And, as I mentioned above, fixity will affect the reactions.
Please refer to the above. I'm learning how to design 2 interconnecting continuous beams. If the beam column connections at the top and bottom were made more pinned.. there would be more moments in the midspan where the beams holding the slab frame into.. this would cause more deflection that would distribute the slabs loads to the ends girder (rather than focusing all at the center). If I made the top and bottom column-beam more fixed.. there are less moments and less deflection at midspan.. this would attract more load from the slabs. In your design which do you prefer?
I guess you will say that depending on the tension bars at positive moments.. there is no problem with deflection if you choose either the pinned or fixed ends of the primary girder. Ok. And depending on the tension bars at negative moments at the continuous ends, you can control approximately the pinned and fixed condition. And these two is what can make the design different.
Well. I let 2 fellow structural engineers design the above. They come out with totally different designs. One guy modelled the ends as pinned while the other guy modelled it as fixed. Since there is no way to totally predict if it will be pinned or fixed and by how much amount, then you should design the center column to be stronger and the girder to avoid unexpected loads. Is this correct? If it is, the it summarizes this thread. Thank Koots for the very enlightening thoughts.
You will note that V2 shading above and to the right of R2 is equal to the V2 shading that goes to the left and below R2. That line running thru R2 (the reaction at R2) is the sum of V2+V2.....exactly what SlideRuleEra told you long ago.....you seem to be arguing with a lot of people who have tremendously more experience than you.....why is that?