Thermal Overload Tripping

Thermal Overload Tripping

Thermal Overload Tripping

(OP)
I have 6 thermal overload relays that frequently trip. They each serve a blower with a 3 Phase 460 V 15 horsepower motor. We measured the voltage at the relays and it registered 510 Volts. Could this be causing the trips?

RE: Thermal Overload Tripping

If your problem is overcurrent, you should have measured the line currents.

RE: Thermal Overload Tripping

Measure the line to line voltages accurately. Unequal line to line voltages will cause greater current inequality. Depending on the impedance of the supply system, a 5% voltage unbalance may cause a 20% or greater current unbalance. The current in the highest phase may be greater than the setting of the O/Ls. Even if your current is not over the rating of the O/Ls, unequal current may be causing differential trips.
Measuring the current is also an excellent idea.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Thermal Overload Tripping

(OP)
Thanks. I will measure the current and the line to line voltages.

RE: Thermal Overload Tripping

Overload relays react to current, not voltage. But if you have motors that are rated for 460V and the voltage applied to them is 510V, that will cause the motor to go into saturation, which increases the current without increasing the work it performs, so of the motor was fully loaded to start with, the high voltage will cause high current and the OLs are protecting the motor. 510V is out of spec for a 460V motor; 460+10% and it is out of spec for the utility supply, 480+5%. You need to address that no matter what.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources