INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you a
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

E-mail*
Handle

Password
Verify P'word
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Member Feedback

"...I just wanted to say that you guys RULE, a million thank you's to whoever created, and/or manages this site. KEEP UP THE GOOD WORK..."

Geography

Where in the world do Eng-Tips members come from?
projectguy (Electrical)
12 Dec 02 15:49
Under the current U.K. regulations is it still neccessary to cross bond pipework below every sink in an installation
Check Out Our Whitepaper Library. Click Here.
Sparkyman (Electrical)
13 Dec 02 18:13
Metal pipework under a sink which connect to the taps have to be considered under BS7671 as 'Extraneous conductive parts', therefore, bond them!
Sparkyman (Electrical)
13 Dec 02 18:22
On second reading you state 'every sink',
If you have a line of sinks in a public toilet for example you would not need to cross bond under each, you would however need to make sure that they are bonded such that there is no potential difference between any mutually accessible conductive parts.
projectguy (Electrical)
14 Dec 02 5:50
thank you sparkyman thats exactly what I thought
Helpful Member!Ahr35181 (Electrical)
3 Dec 03 15:12
Commercial & Domestic kitchens, cloakrooms, bedrooms and toilet areas which may contain a sink or hand basin but do not contain a bath tub or shower are not among the special locations covered in Part 6 of BS 7671. There is usually no reason why such rooms should be considered as locations of increased electric shock risk requiring the provision of supplementary bonding.

The 15th Edition of the IEE Wiring Regulations required supplementary bonding to be applied to all sinks where extraneous-conductive-parts were not reliably connected to the main bonding, and many examples still exist today. This requirement was deleted in subsequent editions of the Wiring Regulations and it is not required by the present Standard, BS 7671.

Alan
jbartos (Electrical)
8 Dec 03 23:34
Suggestion: Essentially, all conductive metallic surfaces are safer to have them bonded since not all of them (not all items) are explicitly covered in standards.
Helpful Member!Ahr35181 (Electrical)
9 Dec 03 5:01
jbartos,

Try telling that to the window cleaners who have been killed by the touch voltage appearing on earthed metal window frames
briand2 (Mechanical)
9 Dec 03 8:08
Things like window frames, in particular, which are likely to be at the edge of the equipotential zone really should not be bonded.  Where there is doubt, the if an insulation resistance ("Megger") test shows that it is at least 2Mohm to earth, then don't bond it!

Otherwise, you'll have to start bonding door handles, coat hooks, etc!

Brian

Start A New Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Promoting, selling, recruiting and student posting
are not allowed in the forums.
Posting Policies

LINK TO THIS FORUM!
(Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum)
TITLE: Electric Power & Transmission & Distribution Forum at Eng-Tips
URL: http://www.eng-tips.com/threadminder.cfm?pid=238
DESCRIPTION: Electric Power & Transmission & Distribution technical support forum and mutual help system for engineering professionals. Selling and recruiting forbidden.