Under the current U.K. regulations is it still neccessary to cross bond pipework below every sink in an installation
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
To cross bond or not to cross bond
|
RE: To cross bond or not to cross bond
RE: To cross bond or not to cross bond
If you have a line of sinks in a public toilet for example you would not need to cross bond under each, you would however need to make sure that they are bonded such that there is no potential difference between any mutually accessible conductive parts.
RE: To cross bond or not to cross bond
RE: To cross bond or not to cross bond
The 15th Edition of the IEE Wiring Regulations required supplementary bonding to be applied to all sinks where extraneous-conductive-parts were not reliably connected to the main bonding, and many examples still exist today. This requirement was deleted in subsequent editions of the Wiring Regulations and it is not required by the present Standard, BS 7671.
Alan
RE: To cross bond or not to cross bond
RE: To cross bond or not to cross bond
Try telling that to the window cleaners who have been killed by the touch voltage appearing on earthed metal window frames
RE: To cross bond or not to cross bond
Otherwise, you'll have to start bonding door handles, coat hooks, etc!