rebar development/lap length
I have a 5' high, 8" thick, cast-in-place cantilever retaining wall. The contractor installed the footing dowels with the vertical leg of the bar 3" too short to have a proper "Class B" tension lap with the vertical bars of the wall.
Is there a procedure to calculate a reduced capacity of the wall based on this improper lap length?
RE: rebar development/lap length
I'd reduce your available steel tension capacity by the same percentage that the lap length has been reduced. Here, that will result in a reduction of moment capacity by the same percentage +/-.
I generally echo KootK's approach. For me though, if the actual bars were #6 (.44 in^2) and As,pro/As,req landed me at .38 in^2, I would round down to .31 in^2 (#5).
"It is imperative Cunth doesn't get his hands on those codes."