ICC 500 / ASCE 7 wind design for safe room
I am designing a small multi-purpose/safe room and ran across an issue. I obtained some calcs from an old job that were done by an engineer that no longer works for my company in order to check my work against hers. I noticed in the C&C section that when she calculated the areas for zone 1, 2, and 3 for the roof deck that she divided the areas by 2. When I looked in the ASCE 7-05 (this is for an IBC 2009 job in a small town) I saw that the figure I used (Figure 6-14A) only covers monoslope roofs with theta between 3 and 10 degrees and Note 5 states that for roofs with theta less than 3 degrees that values of GCp should be taken from Figure 6-11B (Gable roofs with theta less than 7 degrees). Since the diagram in that figure is for a gable roof it has a ridge and zones 1 and 2 are effectively halved compared to a monoslope roof. I am unsure if the area should be calculated for a monoslope (i.e. A = B-2a * L-2a) and then taken to the table in Figure 6-11B or if I should calculate the area as shown in the zone map on Figure 6-11B (i.e. A = (B-2a * L-2a)/2. This is not significant for areas less than 100 sq. ft. as the value of GCp flattens out past that value but for smaller areas like zones 2 and 3 on a small bldg like a storm shelter the result could be effected.
RE: ICC 500 / ASCE 7 wind design for safe room