ACI 318-14, §15.3 - Transfer of column axial force through the.... foundation
Hi to all,
in chapter §15.3 of ACI 318-14 are present rules about the transfer of axial force of column through the floor system, when the compressive strenght of concrete are different for more than 40%. The same rules have to apply also in column to foundation joints?
Thank you in advance.
eng. FERRARI Alberto - www.ferrarialberto.it
RE: ACI 318-14, §15.3 - Transfer of column axial force through the.... foundation
I don't see why not.
When I am working on a problem, I never think about beauty but when I have finished, if the solution is not beautiful, I know it is wrong.
-R. Buckminster Fuller
I think that it's simpler at a footing. It's just straight up bearing and punching shear with some account given to the load transferred via the column rebar dowels.
I feel that it's a bit of a different situation, mechanically, when you're transferring load to a load spreading system like a footing as opposed to passing the load to another column below. Certainly, I'd ensure that bearing worked at the column/footing interface even f'c_coulmn < 1.4 x f'c_footing.
Ohh. At the footing. I don't think it's an issue as long as bearing is satisfied.
I do recall seeing an example problem where they developed the compression rebar into the footing.
Ok, thanks.
I think that §15.3 chapter is not applicable to column-foundation section but I have some doubts about this problem...