Dear all,
Which part of the 132kV XLPE cable will determine the fault level of cable? In other words, when there is a short circuit, which part of the cable (i.e conductor shield, insulation, insulation shield or metallic sheath)will be the most electric stress one.
Thank you!
Which part of the 132kV XLPE cable will determine the fault level of cable? In other words, when there is a short circuit, which part of the cable (i.e conductor shield, insulation, insulation shield or metallic sheath)will be the most electric stress one.
Thank you!






RE: Fault level of cable
RE: Fault level of cable
So far as electrical stress goes, though, well, that's the whole point of having insulation and insulation shields, to ensure that the entire field drops across the insulation.
RE: Fault level of cable
a) If the cable is shielded, shield be able to handle and maintain its integrity under specified short circuit level. Cable vendors provide standard cable products, therefore you must specify your shield cross-sectional area or indicate tha the cable must comply with your kA requirements and provide data to support it.
b)Cable if braced in trays, etc must comply with certain separation requirements ( distance between supports points ) these will change with the max. possible short circuit value. European standards such as VDE have formulas for this, but also some IEEE-IAS papers have addressed the subject.