Wound Rotor Secondary Current vs Brush wear
Wound Rotor Secondary Current vs Brush wear
(OP)
I have a couple of 6,000 HP wound rotor motors that are using a lot of brushes. Besides the cost and maintenance of the brushes, the resulting carbon dust is killing my motors. I have had several failures of these motors over the past ten years or so. We also have to pull the motors and do full PM's on them on a regular basis to mitigate the carbon from the windings
We did hook up a CT with a recorder and got about 600-700 Amps on start and 50-60 running. Meanwhile we have 11 brushes per phase and I believe each one is rated about 200 amps. We have started to remove some of the brushes but there has to be a reason why I have so many brushes. Brush life is only a few months.
Why do the motor manufacturers provide the motors with such a high brush load? I have motor from two different manufacturers and both have about the same amount of brushes..
any thoughts?
We did hook up a CT with a recorder and got about 600-700 Amps on start and 50-60 running. Meanwhile we have 11 brushes per phase and I believe each one is rated about 200 amps. We have started to remove some of the brushes but there has to be a reason why I have so many brushes. Brush life is only a few months.
Why do the motor manufacturers provide the motors with such a high brush load? I have motor from two different manufacturers and both have about the same amount of brushes..
any thoughts?





RE: Wound Rotor Secondary Current vs Brush wear
I had a similar problem on a wound round some years ago. I worked with Helwig and they recommended a different brush which lasted much longer.
Attached is a guide from Helwig. This might help. They have a lot more troubleshooting guides on their website. It would also be helpful to send a used brush into Helwig for review.
EE
RE: Wound Rotor Secondary Current vs Brush wear
RE: Wound Rotor Secondary Current vs Brush wear
I out a CT on one phase of the buss connections feeding the Liquid starter (there is only one per phase)
Starting method is a Liquid Starter
RE: Wound Rotor Secondary Current vs Brush wear
when the motor with wound rotor is working secondary or rotor current is almost DC and frequency is in Hz parts so it can not be measured by traditional AC instruments .That is why I think the results of measuring currents are fake .
Usually such a big motor have a device that upon completion of the start raise the brush and make a short outputs of winding rotor but your motor unfortunately do not have it .
Good luck !
RE: Wound Rotor Secondary Current vs Brush wear
What happens sometimes is that this information gets lost as personnel changes and new people are never properly instructed on that issue. Then if the operation changes where the motor is no longer running continuously, the new crew changes ALL of the brushes at the same time, then let's them get too low before changing again because of the cost. Waiting too long befor changing can accelerate the brush loss toward the end, which results in extreme carbon release.