Soft Start Feeder
Soft Start Feeder
(OP)
The question has come up as to how to size the feeder cables to a motor circuit with a soft starter per the NEC. It would seem that article 430.122 would apply and that, with a bypass circuit, the feeder needs to be sized by 125% of the soft start rating or the motor FLA, whichever is higher. But the language of 430.122 says "adjustable speed drive" rather than just "power conversion equipment". Some soft starts work much like a cycloconverter so in that respect they could be qualified as "adjustable speed" but most are just a voltage chopper so the language would seem to not apply. But the logic for sizing based on the device rating does make sense to me. Is there any CLEAR guidance on if 430.122 applies to soft starts or anywhere else that soft start feeder sizing is defined?





RE: Soft Start Feeder
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
RE: Soft Start Feeder
Also, while Part X is titled "Adjustable Speed Drive Systems" it describes in multiple locations "Power Conversion Equipment" for which an active solid state switching device such as these soft starters would appear to apply. At the very least, the logic seems consistent that if the device is capable of drawing a higher current continuously it should be fed by a circuit sized on that basis. But the NEC language, in my opinion, is ambiguous on this topic.