Help with embedding wood post into concrete footing
Hi Folks ... I am not a structural engineer thought posting to this site could get me in right direction. Looking to support a deck in Michigan, hired a local structural engineering firm to do the post/beam and footing sizings and although most of work seemed okay, was advised to embed a 6x6 wood post into the bottom of a 36 inch Bigfoot form with a 14 inch Sonotube sleeve over the top.
This seemed to not pass the smell test ... I suspect putting a 6x6 post to the bottom of the form severely weakens the structure. Also, lots of people around here feel embedding posts (even pressure treated) is less robust than posts anchored to footings above grade. I contacted the manufacturer of the Bigfoot form system and they advised against putting the post to the bottom of the form.
Looking thru the calculations of engineer hired for job, vertical load on the footing is 16682 lbs. I found a round footing sizing chart (google) and for 2500 PSF soil conditions a 36 inch footing is needed. My suspicion is this table assumes 2500 psi homogenous concrete footing with centered axial loading (straight vertical load).
I cannot seem to find any info on how to design a bell shaped concrete footing with an embedded wooded post. Is there such a thing? Perhaps a simpler footing design is in order (like a rectangular shape with steel reinforcement). Since this project is for my home and I plan to live here until I die, I would like to construct these footings in a robust manner. I should add footing depth is 42 inches minimum for this area and that the height of the posts above grade will be about 11 feet. Soil has been tested (silty clay) and will withstand 2500 PSF. Deck will attach to structure of house.
Where can I find info on proper design techniques?
RE: Help with embedding wood post into concrete footing
1) The post being in direct contact with the ground.
2) Potential for water to get in to the system where the wood enters the concrete.
Can you just ask the structural engineer to revisit this? It's hard to imagine that they'd object.
What kind of a structure is this? The only reason that I can think of for embedding the post is to attempt to create a moment connection at the bottom of the post which is rare.
Interestingly enough there seem to be lots of differing opinions on viability of a pressure treated wood post embedded in a concrete footing on this website. Assuming for a minute I wanted to accept the shortened life, is there some approved way to do that? What is the publication where this is covered?
Also, if I don't embed the posts, I think the connection has to be treated as "pinned" so it cannot react any moments only axial loads? I am guessing that with the height of the posts being 11 feet and the fact they have eccentric loading at the top (triple 2x12's bolted to the knotched post) there may be a need to either increase post size above 6x6 or embed to avoid buckling of the posts (column).
If there is anything else that you could suggest I read that would help me I would appreciate it. Intuitively this seems like a very common design detail for residential so I cannot believe I have to invent a new wheel here. Thanks again for your comments. My idea here is to try to look at all the alternatives and have a couple that I like before I go back and challenge the firm doing this work.
Is there a way to spread the load at base of the footing and still embed the post or is that just not done?
I doubt it. This would be pretty atypical.
I wouldn't waste your time. Ask for the top mounted detail or an explanation for why the embedded detail is required. The top mount detail should be cheaper to build and more durable. It's a no brainer in my opinion.
http://www.strongtie.com/literature/c-c-2015.html
The attached may be of some help. There are some foundation details.
I agree with graybeach; I would attach the column at the top of the pier. Suppose the posts have to be replaced some day? If you embed the posts you would have to tear out the foundation to replace them. If your columns are pinned, no big deal, that's why we have bracing.
Assuming there's no local law requiring PT wood it's your property; just consider the future if you're planning to sell the house.
I would recommend using a Simpson baseplate. The tradeoff is that you lose some fixity at the base, but the post will last much longer.
When I am working on a problem, I never think about beauty but when I have finished, if the solution is not beautiful, I know it is wrong.
-R. Buckminster Fuller