Class 1E power feed separation

Class 1E power feed separation

Class 1E power feed separation

(OP)
If I have a component that must receive class 1E power, how far upstream does that circuit need to be class 1E?IE, all the way to the Unit Auxiliary Transformer?

thanks

RE: Class 1E power feed separation

Generally, you're considering that Class 1E circuit traces back to the buss that is supplied by your emergency diesels. In our plant, our Class 1E buss is 4160V. It is normally fed from offsite power, which is NOT Class 1E. But, in the event the offsite power feed is lost, the emergency diesel generator supplies the power to the Class 1E buss. All of the components associated with the EDG's are safety related, thus assuring that you can provide power to the Class 1E equipment. Your unit aux transformer is likely NOT safety related.

So, for example, our Class 1E buss is 4160V, which feeds some important pumps, etc. and several 480V load centers. Those load centers then feed multiple other components and some 480V/240V/120V transformers that feed to other components/circuit panels. All of this is considered Class 1E. We also have similar systems that are not considered Class 1 to feed circuits that do not have safety related equipment/components. The primary difference is that the non-Class 1E systems do not have the backup emergency power supplies. So, if we lose offsite power, the non-Class 1E circuit will not have power.

RE: Class 1E power feed separation

(OP)
thank you jpankask. Great explanation. So, for example, if I have a Class 1E field instrument with Class 1E wiring/connections to a local instrument panel (also 1E) but then power wiring from that local panel to distribution panelboards which are non-Class 1E, that would pretty much make having a 1E field instrument and wiring to local panel pointless wouldn't it?

thanks

RE: Class 1E power feed separation

Yes it would be pointless, and much more expensive than it needs to be. At our plant, everything in the Class 1E system is Class 1E, i.e. you wouldn't have Class 1E system down the distribution panel, then non-Class after that, because the non-Class 1E equipment could compromise the integrity of the Class 1E system.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources