Bottom plate failures at SWS tension chords

Bottom plate failures at SWS tension chords

(OP)
During inspections and plan review I have noticed the engineer allows 8" -12" from the corner holddown anchor bolts to the 2-2x4 chord of a wood SWS.
It seems the moment on the plate which is acting as a cantilever is much higher than designed for.Also the shear is higher than a 2x4 can take( especially on multistory buildings using type 1 SWS.)
Am I off base here? I recall these failures in testing.

Inspector Jeff

RE: Bottom plate failures at SWS tension chords

I don't do many wood frame shear walls, but that sounds suspicious. When specifically designing shear walls, I always pass by the mud sill with Strong-Tie HDU's or similar.

"It is imperative Cunth doesn't get his hands on those codes."

RE: Bottom plate failures at SWS tension chords

The Canadian code allows this for a certain range of load.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Bottom plate failures at SWS tension chords

I see this called out often, but I normally see an accompanying note adding a double stud adjacent to the holddown and providing edge nailing to the double stud.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close