Wind load over rive
Wind load over rive
Wind load over rive
Is wind load any different at river shore or middle ogf river compare to the land at low elevations? Can we use the ASCE7-05 land values in ASCE for objects floating on water?
Thank you
RE: Wind load over rive
I'd say you could use it but watch those exposure categories. How wide is the river from bank to bank and are there any straight portions that you might get exposure C or D in?
Any valleys or hills that might cause increased wind effects?
Maine Professional and Structural Engineer. www.fepc.us
TehMightyEngineer (Structural)
The River is 4,400feet wide bank to bank
If the fetch distance across water does not exceed 5000 feet, then ground conditions prevail. Check the ASCE 7 definitions.
It's not just across the river. It's parallel to it too. Any direction...
Mike McCann, PE, SE (WA)
Ron (Structural,
Thank you very much but could you please referece the section chapter of ASCE that says that please?
Is it on ASCE 7-05 or ASCE 7-10?
I dont have the code, I need to ask someone copy that particular page for me
Thank you so much.
ASCE 7-10 p. 251
On a related note, I've always found it curious that the topographic adjustment factor only applies to "negative curvature" features (hills, ridges), and not "positive curvature" features like river valleys. Anyone know why that is?