Types Of Relay Contacts
What are the differences between a (Form A), (Form B), (Form C) relay contacts?
Is there such a thing as a "wet contact" as opposed to a "dry contact"? If so, what is a "wet contact"?
RE: Types Of Relay Contacts
b = normally closed (NC)
c = 1 NO & 1 NC with 1 common lead (3-wires)
dry contact = just a plain old contact, any configuration. Some other power source is required to use a dry contact. In contrast, some devices switch an internal power source and can drive a load directly with nothing more than a pair of wires required. You need to supply a separate power source with a dry contact.
wet contact -- I've never heard that term used, although it would seem to naturally follow from "dry contact".
The terms “wetting voltage” and “wetting current” are used for signaling circuits in telecomm.
A "wet" contact would be a contact that is energized from a local voltage source. This is sometimes done when providing a contact input to a remote device that is designed to detect a voltage difference but does not provide a source of power for the contact input.
This is sometimes an issue with PLC and DCS inputs. Some types want only dry contacts and supply the interrogating voltage internally, while others need a remote voltage source.
Hope that helps.
The C-form contact is sometimes referred to as the three-way switch or the transfer switch.
Contacts that are operating frequently usually survive due to a wiping action on the contact surfaces as they open and close.
Best regards,
Mark Empson
http://www.lmphotonics.com
A dry contact probably does not have any "official" assigned and agreed upon definition. However there is by my experience a rather simple and reliable definition that most people in my industry agree upon.
When two control systems are present, each having its own voltage and signals that must never touch each other, a dry contact allows one system to signal the other system without any direct wire connection between the two. This signal is achieved by a relay. The coil of the relay is operated by one control system, while the contacts are read by the second control system. There is no direct connection or circuit between the two systems.
If others disagree then please tell me because I have never seen anyone disagree with this definition.
Richard Neff
Richard Neff
Irrigation Craft
Dry refers to the fact that the control system operating the coil of the relay has no wires involved with the contacts of that relay, therefore the contacts are "dead" or "dry", they have no voltage on them. That way the second control system can safely connect to any of the contacts of that relay without any danger of receiving voltage from the first control system.
Richard Neff
Richard Neff
Irrigation Craft
1. IEEE Std 100-2000 "Dictionary.."
Dry contact is one through which no direct current flows
Wet contact (telephone switching system) is one through which direct current flows. Note: Term has significance because of the healing action of direct current flowing through contacts.
1. Could someone explain the IEEE references to me? I do not have that document or easy access to it.
2. I am sure that jbartos knows something I do not, but could jbartos elaborate more? For instance, has jbartos
seen the concept used as I explained it? Would I be advised to stop using the term in the manner I described.
3. Also, what does jbartos and the IEEE mean by "Dry contact is one through which no direct current flows"? I can think of a few misinterpretations such as:
Does this mean low current or direct current as in the opposite of alternating current?
I hated to ask all those questions but I am determined to get this right and if need be correct my understanding.
Thank you,
Richard Neff
Richard Neff
Irrigation Craft