Hello,

Can someone please tell me if an ungrounded 13.8kV system is allowed by the NFPA/NEC requirements.

I have read the NEC code but cannot find any definite answer.I may be missing something ofcourse.

Can anyone please advise and hopefully point to the specific article.

Thanks

RE: Ungrounded MV System - NFPA

Check 250.20(C). Not required unless it serves mobile or portable equipment.

RE: Ungrounded MV System - NFPA

(OP)
Thankyou for that.

Do all ungrounded systems require earth fault detection?

Would a 13.8kV ungrounded system require one?

Also can someone provide a link or brand/model of equipment that has ground fault detection at MV

RE: Ungrounded MV System - NFPA

Really depends on the insulation rating of your equipment. IIRC, you are not required to trip the system if your insulation is rated 173% of the system voltage. You can set your ground fault detection to alarm and locate the faulted section. If your equipment voltage rating is 133% of the system voltage, you are required to set your ground fault protection to alarm and time the tripping within 1 minute to an hour. If your insulation ratings are 100% of the system voltage, you are required to alarm and trip the system within 1 minute before your equipment gets damaged by overvoltages.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources