NFPA 13R 6.6.5.1
NFPA 13R 6.6.5.1
(OP)
The attached file shows an isometric elevation and code reference for NFPA 13R 2013 6.6.5.1. We have a covered stairwell and covered entry to the apartment unit. This is a 2 story Type V construction multi-family building. The AHJ suggests the roof overhangs the stairs and entryway and needs to be protected. It is the AHJ's opinion that the overhang is covering "by definition" a patio/balcony and requires protection.
Any thoughts? Is this any clearer in an NFPA 13R handbook?
Any thoughts? Is this any clearer in an NFPA 13R handbook?





RE: NFPA 13R 6.6.5.1
I recently ran into the same problem but didn't fight it because I got paid extra to do it. I never fight someone who wants to give me more money.
That said my lowly opinion is they should get rid of all Type V construction altogether.
RE: NFPA 13R 6.6.5.1
SD2, you will never get rid of Type V construction in Group R. Too much money is on the table.
RE: NFPA 13R 6.6.5.1
Dry pendents and dry sidewalls, all 60 of them where I had 20 originally figured.
I am an experienced (40 years) layout technician and I never, ever make the decision as to whether the project is covered by 13 or 13R. If residential I want to see something exactly like this
or a written letter signed by the building professional telling me, the certified layout technician, exactly what standard I am to follow and that is exactly what I do. This way if someone comes along later saying the project needs a full 13 system I am not the dead dog laying in the street but the guy with a very legitimate, and big as in BIG, change order coming my way. Thank you very much.
And that is my two cents worth.