Differential protection, different CTs

Differential protection, different CTs

Differential protection, different CTs

(OP)
Talking about high impedance differential protection, would a higher min. pickup current compensate the lower CT class? say 5P20 instead of CLX?

I understand that this will compromise the protection accuracy but still be of very satisfactory for in zone faults esp. with solidly grounded wye-wye.

any clue?

RE: Differential protection, different CTs

Pick-up is always minimum in terms of time and you will need to calculated a voltage accross relay resistor that results due to external faults, so your relay can ride through external faults. So whats the advantage of using a high impdennce differential if you are going to compromise on CTs. Go with C800. Or use partial differential scheme using overcurrent relays with 5P20 CTs

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources