Shoring load on 5" slab on grade
The shoring contractor has indicated diagonal braces to existing basement wall where portions of the first suspended parking floor above the basement slab-on-grade will be temporarily removed during repair of the suspended floor. I calculate that the lateral force the shore will have to take is 21000 pounds. (The diagonal shores are 3 foot on centre; 3 x 7000 = 21,000). The diagonal shores which are at 45 degrees to the horizontal therefore will each apply 21,000 pounds as a vertical load to the 5" slab-on-grade. The diagonal shore has a 10" x 12" x 1/2" steel plate at its base. This load seems too much for a 5" slab-on-grade even if there were 100 pci soil modulus. Any comment?
Also there use to be on the internet a place were you could call up the Westergaard equations and plug in the numbers and it would give the slab stress, but I cannot find that now. Anyone know how I could get to that, or similar?
RE: Shoring load on 5" slab on grade
Anyone got a spread sheet or know of one for Westergaard, or an internet place that has? I wrote one a long time ago, but I don't entirely trust it for high loads.