Dear Fórum:

Sprinkler with K5.6 are permitted for protecting storage if the criteria is density/área (OH-2 in my case), even thou they are not specifically listed for protecting storage.

I am correct?

thanks

RE: K5.6 sprinkler for storage

See NFPA 13-2013 12.6.1. 5.6k is acceptable until your density exceeds 0.2 gpm/sf.

R M Arsenault Engineering Inc.
www.rmae.ca

RE: K5.6 sprinkler for storage

(OP)
Thanks skdesigner, for the confirmation

regards