Series ratings and bus bars

Series ratings and bus bars

Series ratings and bus bars

(OP)
When reading about series ratings I often see mention of fuse-fuse, breaker-breaker, and fuse-breaker series ratings. Two questions about this:

1.) This first question is in regards to the NEC specifically:
Since series ratings are mentioned under part VII. of Article 240 and not under sections V. or VI., does this mean that series ratings only exist when the load-side device is a circuit breaker. In other words, fuse-fuse series ratings do not exist or rather are not permitted by the NEC even if there was some tested combination that passed a UL test for series ratings?

2.) Can current limiting fuses be used to allow the use of bus that has a withstand rating lower than the available short circuit current.
For example, from a NEC requirement and technical soundness perspective, would the following scenario be adequate:

UL891 Switchboard
100kA 3 cycle bus bar withstand rating
200kA interrupting rating current limiting fuse upstream of bus bar (main disconnect)
200kA interrupting rating protective device downstream of bus bar (branch disconnect)
150kA available short circuit current on line side of main disconnect
And for argument sake assume the peak let through current of the current limiting fuse is less than 100kA.

My thoughts are from a strict code perspective this would not be allowed because the short circuit current rating (SCCR) 'shall not exceed the interrupting rating or short-circuit current rating of any component in the power circuit' (from NEMA PB 2-2011) and this, in my opinion, specifically includes (among possibly other things): individual protective device interrupting ratings, interrupting ratings for series rated protective devices (see question 1 above), and bus bar withstand ratings. Thus, the switchboard SCCR would be 100kA due to the withstand rating. From a technical perspective, and where the NEC or other code did not apply, I think some people may find the installation acceptable because the bus bars are a 'passive device' not subject to dynamic impedance thus the 'up-over-down' method could be used. Thoughts?

RE: Series ratings and bus bars

(OP)
Clarification:

I don't agree with using the let through current for evaluating the acceptability of the bus bar withstand rating because if the fault is on the load side of the branch overcurrent device then that device will invalidate the accuracy of the published let through current curve for the upstream current limiting fuse. I mentioned the view point because I know some people have that view.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources