HCL off gas
HCL off gas
(OP)
We store 36% HCL inside in one of our processing buildings. The scrubber had leak and we off gassed HCL through the building. This has caused the galvanized conduits and piping to rust plus coat MCC. We taken samples on the inside of the MCC and no evidence of HCL. My questions are do I need to get the residue off of the conduit, pipe, and MCC and if so with what? After I get the residue what sort paint or coating should I reapply onto these? Is there some sort of sniffer to install to alarm us if this occurs again? I can mitigate the MCC by making sure the door is closed.
Thanks in advance.
Chip Fuller
Thanks in advance.
Chip Fuller





RE: HCL off gas
Pressure wash with copious amounts of pH neutral water? Contact Sherwin Williams, Behr, PPG or Glidden on the type of coating. I'm sure you can google HCl detectors and get millions of hits. We have detectors, but not for HCl.
Good luck,
Latexman
Technically, the glass is always full - 1/2 air and 1/2 water.
RE: HCL off gas
As said, wash up with water until neutral, or if highly acidic, a soda ash solution can be used to neutralize.