Reinforcing requirements based on % of concrete volume
I am working on a budgetary number for a parking ramp. The large footing pads do not have an actual rebar design yet, but there is a note stating that the reinforcing requirements shall be 1% of the concrete volume.
The sizes are as follows:
10-0 x 10-0 x 28" (8.641975 CY or 233.3333 CF)
12-0 x 12-0 x 32" (14.22222 CY or 384 CF)
14-0 x 14-0 x 36" (21.77778 CY or 588 CF)
20-0 x 20-0 x 42" (51.85185 CY or 1400 CF)
25-0 x 25-0 x 48" (92.59259 CY or 2500 CF)
20-0 x 31-0 x 48" (91.85185 CY or 2480 CF)
31-0 x 20-0 x 48" (91.85185 CY or 2480 CF)
34-0 x 20-0 x 48" (100.7407 CY or 2720 CF)
How do you go about calculating what the rebar would be? In my experience in jobs of this size, the footing pads have a double layer of rebar (one top and bottom).
If you need any further information from me, please let me know.
Chris
RE: Reinforcing requirements based on % of concrete volume
1% of concrete volume (for steel volume) seems simple to me. Whether the estimate proves correct or not will be known once the design is done.
Dont know if this will help but I came across a conversion factor by weight for unknown rebar.
Multiply your CF x 165= x tons/2000 lbs per ton = tons of concrete w/ rebar.
Your example:
233.33 x 165 = 38499.45 / 2000 = 19.249 tons
Let me know if this does anything for you.
frostryan's conversion factor is well off the mark. 1% of 233.33 CF is 2.33 CF of steel, which weighs about 1140 pounds. I have no idea if that is what the footing requires, but that is what the note says.
generally require area of steel as a percentage of the area of the structural element. not sure how volume of steel entered into the picture.
What I have done previously is take a fully designed, similar structure, calculate the weight of steel for that structure as a percentage of the concrete volume and use that number for estimating. Say 140 lbs steel per cubic yard which will give you a fairly heavily reinforced structure such as a box culvert
cvg,
The 1% volume would give 132 pounds/CY, so not far from your estimating value.
frostryan's formula essentially says that rebar is 4.4% by volume (or given a prismatic section, this is the steel area as a percent of gross area of section).
If you subscribe to a unit-weight-of-reinforced-concrete formulation such as frostryan's, a bunch of algebra yields the following:
Vs ≡ (w-wc)/(ws-wc)*V [EQUATION 1]
Where V = Total volume of reinforced concrete element
Vs = Total volume of steel in the element volume
w = unit weight of total volume (= 165 lb/ft3 according to frostryan's formula)
wc = unit weight of concrete (= 150 lb/ft3 - a typical value)
ws = unit weight of steel (= 490 lb/ft3)
This seems pretty steep to me, but ymmv. It would probably be useful to run a bunch of typical concrete elements that you use in your particular application and see what you come up with.
If you calculate the weight of your steel for a given concrete volume, you can then calculate "w" as follows:
w = Ws/(ws*V)*(ws-wc)+wc [EQUATION 2]
Where Ws = Total weight of reinforcement for a given total volume V.
You'd then have a handy-dandy value for "w" (again, in frostryan's example w = 165 lb/ft3) to plug into EQUATION 1, to estimate your steel weight from a given volume of concrete. I suggest this calculation is idiosyncratic to the typical types of concrete elements you deal with, and your particular detailing preferences. But if you have a large enough "database" against which to apply EQUATION 2, then EQUATION 1 would be a very handy formula. I'd suggest having a value of "w" for beams of s certain size, another for columns (possibly by type), another for slabs, and so on.
OH...simply multiply the result of EQUATION 1 by ws (= 490 lb/ft^3, e.g.) to obtain the WEIGHT per unit volume, since you typically want that value rather than just the volume:
Ws = ws*(w-wc)/(ws-wc)*V [EQUATION 1a]
That variable "w" is the linchpin for the whole procedure.
"No one is completely useless. He can always serve as a bad example." --My Dad ca. 1975
hokie66 "The 1% volume would give 132 pounds/CY, so not far from your estimating value"
If you assume 1% by volume (or area of prismatic section - which incidentally is the minimum reinforcement required for a column by ACI 318), then:
w = 0.01(ws-wc)+wc = 0.01*(490 lb/ft3 - 150 lb/ft3) + 150 lb/ft3
= 153.4 lb/ft3
(Compare with the value of 165 given in frostryan's formula).
I cannot believe that this is causing so much angst.
If the concrete volume is 233.33ft3 and steel weighs 490lbs/ft3, then at 1% reinforcing by volume
steel reqd = 1 / 100 *233.33 * 490 = 1143lbs.
What has concrete density got to do with it?
rapt...we can overthink anything! hokie66's first answer was the right one and nothing necessary beyond!