Hello all,

I'm looking for any advice/comments on using multiple hot water recirculation pumps for domestic hot water systems. The intent is to use two pumps (one for each extended recirc main serving the farthest fixture at opposite wings) back to the cold water main tying to the hot water heaters (in my case, a total of 3). The concern I have is the overall performance of the recirc system when using multiple pumps (ie: will they be potentially fighting one another). I am curious if anyone out there used them in their design of the hot water recirc system.

Thanks,

RE: Multiple Recirculation Pumps for Domestic Hot Water Use

I could swear I've seen it done, as much as 50 years ago, but my memory is pretty dim these days.

I don't think I've seen the hot water return directed to the cold water main, which I'd guess would eventually get you warm water in the cold water system.

How about returning the hot water loop to the top of the hot water tank?

No expertise claimed here.

Mike Halloran
Pembroke Pines, FL, USA

RE: Multiple Recirculation Pumps for Domestic Hot Water Use

I don't understand why you don't just tie it back to the tank but so long as there are common inlets and return points, each loop should be able to work independently without impact on the other. A quick sketch of your system would be good to make sure my understanding is correct.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Multiple Recirculation Pumps for Domestic Hot Water Use

I won't say it has never been done, but common practice is to use a single pump, sized for the longest (or most pressure loss) portion. Flow rate is based on heat loss through the insulated piping. Balancing valves are placed on the other loops to prevent short circuiting. You have to tweak the pump flow rate to account for the extra loops, but that doesn't add too much and if your piping is sized correctly, the pressure loss from the additional flow is not significant.

In a multiple pump situation, one of the pumps is going to be nearly identical to the pump in the single pump situation, so the second pump is mostly redundant. Other than the balancing valves and maybe a little bit of piping, the single pump system will be less expensive.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources