Hi,

I need to install 2 new fumehoods in a Lab that already contains 20 Fumehoods.
I've been told the AHU is maxed out & can't support any more fumehoods.

I have scope to replace some of the larger old fumehoods with smaller Fumehoods.

I want to know if the maximum amount of fumehoods is a function of the Design Volume of each fumehood or the amount of space open to the Lab at each fumehood sash.

Basically, can i replace a large fumehood of volume X with 2 smaller fumehoods of Volume X/2.

Thanks
KC

RE: Installing Fumehoods In a Lab

You have to approximately the same air volume entering the building as exiting the building.

If you do not enough makeup air, it will hard to exhaust. You also will a have time opening doors to the building.

Replacing a large fumehood of volume X with 2 smaller fumehoods of Volume X/2 is acceptable.

RE: Installing Fumehoods In a Lab

When I've done fume hoods, the face velocity of air across the sash was the critical value for air handling, not the contained volume of the hoods.

RE: Installing Fumehoods In a Lab

What I meant to say above is that the exhaust flow in CFM is the important parameter if you want to change the size of the hoods. The building HVAC system has to allow enough air into the building when the fume is operating. The building should be slightly pressurized. If the building had negative pressure from too much exhaust flow, the exterior doors would be hard to open and the fan would have a hard time pushing out the exhaust.

77JQX is correct in stating that the face velocity is important, but that issue has to do with the capture of the fumes.

RE: Installing Fumehoods In a Lab

(OP)
Thanks for the replies above

KC79

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources