Need help understanding the ratings of an existing neutral grounding reactor -

It is installed on the neutral of a D-YG transformer, 13.2KV L-L.

The documentation states it is rated 5.99 ohm, 15.9 mH, 100A, 7.6 KV, 60 Hz.

What does the 100A rating signify? 5.99 ohms at 7.6 KV would suggest much higher currents. Is this a 10s rating?

RE: Transformer Neutral Grounding Reactor

Most NGRs are designed to carry rated current for 10 seconds, IMHO. 100A rating means the NGR allows 100A at 7.6 kV for 10 seconds. To prevent damaging your NGR, please check if your protection trips earlier than 10 seconds.

Hope that helps.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources