ASCE 7-05 Minimum Wind Load
For ASCE 7-05 - Method 2 Heights less than 60' what is the minimum wind pressure.
I was under the assumption that it would be 10psf, however I cannot find this provision in this section. It appears the only reference to a minimum is that you would neglect any net negative wind pressures. Does this sound correct or am I missing something?
In ASCE 7-10 they have a minimum 10psf on walls and 5psf on roofs (again I don't see this in -05 version).
Thanks!!
EIT
www.HowToEngineer.com
RE: ASCE 7-05 Minimum Wind Load
The minimum wind pressure requirements are in Sections 6.1.4.1 and 6.1.4.2. These are valid regardless of which Method is being used for the main wind analysis. The 2005 values are 10 psf across the board, no reduction for the horizontal projection of the roof as indicated in ASCE7-10
Note the ASCE7-10 minimum wind values are now 16 psf and 8 psf, not 10 and 5.
Yes, but if you convert the 16 and 8 psf to ASD you are basically back to 10 and 5 psf.
A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com
@ajh1 -> Thanks, I completely missed the opening section.
Yes, I was converting the wind pressures from ASCE 7-10.
EIT