Heat load calculation

Heat load calculation

Heat load calculation

(OP)
We have a 600V 3 phase 500 KVA motor generator set.  I need to do a calc to determine how much this unit loads the A/C system for this building.  I have all the electrical data for the motor and sychronous generator.  Where can I find guidance on how to do this calc?

RE: Heat load calculation

You can if you have any two of the three values Out, In, Efficiency.  If the machine is running you can certainly measure the electrical power input and output precisely with the right equipment.

Out = Motor Generator Output Power
In = Motor Generator Input Power
Losses = Power Dissipation to be removed by ac

If you have output and input power:
Losses = In - Out

If you have In and Eff
Eff = Out/In = (In-Losses)/In
In * Eff = In - Losses
Losses = In*(1 - Eff)

If you have Out and Eff
Eff = Out/In = Out/(Out+Losses)
Eff*Out+Eff*Losses = Out
Losses = Out * (1/Eff-1)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources